We do enough Navy work where we're seeing test headers on every project now.  
Same set-up as a pump test or wall hydrant.  


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Matthew J. Willis" <[EMAIL PROTECTED]>

Date: Fri, 30 May 2008 09:00:46 
To:<[email protected]>
Subject: RE: 200 psi test for components rated 175


Trick question huh? Some would argue reversing the FDC check, and flowing
 there from..
 
 R/
 
 Matt
 
 Matthew J. Willis
 Living Water Fire Protection, LLC.
 1160 McKenzie Rd.
 PO Box 877
 Cantonment, FL. 32533
 850-937-1850 Voice
 850-937-1852 Facsimile
 [EMAIL PROTECTED]
 
 
 ----- >-----Original Message-----
 ----- >From: [EMAIL PROTECTED]
 ----- >[mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> ] On
 ----- >Behalf Of Fletcher, Ron
 ----- >Sent: Friday, May 30, 2008 10:47 AM
 ----- >To: [email protected]
 ----- >Subject: RE: 200 psi test for components rated 175
 ----- >
 ----- >six
 ----- >
 ----- >-----Original Message-----
 ----- >From: [EMAIL PROTECTED]
 ----- >[mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> ] On
 ----- >Behalf Of Gregg Key
 ----- >Sent: Friday, May 30, 2008 8:37 AM
 ----- >To: [email protected]
 ----- >Subject: Re: 200 psi test for components rated 175
 ----- >
 ----- >Speaking of such test, How many systems are installed
 ----- >with a means to test the backflow at the required
 ----- >forward flow rate? like a wall hydrant?
 ----- >
 ----- >Thom McMahon wrote:
 ----- >> Don't forget the derided full forward flow test!
 ----- >>
 ----- >> -----Original Message-----
 ----- >> From: [EMAIL PROTECTED]
 ----- >> [mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> ] On
 ----- >Behalf Of Steve
 ----- >> Leyton
 ----- >> Sent: Friday, May 30, 2008 8:42 AM
 ----- >> To: [email protected]
 ----- >> Subject: RE: Re[2]: 200 psi test for components rated 175
 ----- >>
 ----- >> So it's contractual, not philosophical.   Presumably,
 ----- >the installing
 ----- >> contractor tests it ...
 ----- >>
 ----- >> I don't think we're talking about testing the backflow
 ----- >appliances
 ----- >> itself for functionality - that's best left for the "certified
 ----- >backflow
 ----- >> technician."   If you pump up an UG including the BFP,
 ----- >the relief
 ----- >valve
 ----- >> will only operate when there's a differential between
 ----- >the clappers. 
 ----- >> So an RPZ or RPDA usually weeps a bit when you pump it
 ----- >up, but once
 ----- >> the line is equalized you can run a conventional
 ----- >hydro.  And if you
 ----- >> just want to test against it, you can pump up through
 ----- >the FDC or main
 ----- >> drain or the supply-side tap on the riser check, if so
 ----- >equipped.
 ----- >>
 ----- >> Steve Leyton
 ----- >> Protection Design & Consulting
 ----- >>
 ----- >>
 ----- >> -----Original Message-----
 ----- >> From: [EMAIL PROTECTED]
 ----- >> [mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> ] On
 ----- >Behalf Of Coastal
 ----- >> Sent: Thursday, May 29, 2008 7:10 PM
 ----- >> To: Steve Leyton
 ----- >> Subject: Re[2]: 200 psi test for components rated 175
 ----- >>
 ----- >> Hello Steve,
 ----- >>
 ----- >> I start 1' AFF with my work. I sub out any underground
 ----- >installation
 ----- >> work I get (which I try to avoid) and it is up to them
 ----- >to test it.
 ----- >> Only question I have is how do you get an RPZ to hold the back
 ----- >> pressure to hydro to it? Pump the system up through
 ----- >the #1 test cock?
 ----- >>
 ----- >> --
 ----- >> Best regards,
 ----- >> Charles Thurston
 ----- >>  Coastal                           
 ----- >mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> 
 ----- >>
 ----- >> Thursday, May 29, 2008, 6:55:37 PM, you wrote:
 ----- >>
 ----- >>> I'll bite - why not?   If the Fire Department pumps
 ----- >into the FDC,
 ----- >> isn't
 ----- >>> it likely to back pressure the BFP to at least 150? 
 ----- >And if so,
 ----- >> wouldn't
 ----- >>> it be prudent to test the assembly?
 ----- >>
 ----- >>> Steve Leyton
 ----- >>> Protection Design & Consulting
 ----- >>
 ----- >>
 ----- >>> -----Original Message-----
 ----- >>> From: [EMAIL PROTECTED]
 ----- >>> [mailto:[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> ] On
 ----- >Behalf Of
 ----- >>> Charles Thurston
 ----- >>> Sent: Thursday, May 29, 2008 3:30 PM
 ----- >>> To: IPA
 ----- >>> Subject: Re: 200 psi test for components rated 175
 ----- >>
 ----- >>> Hello IPA,
 ----- >>
 ----- >>> I for one have never put 200 on the backflow, I will
 ----- >not either.
 ----- >>
 ----- >>> Thursday, May 29, 2008, 6:03:25 PM, you wrote:
 ----- >>
 ----- >>>> I've got this question posed to me:
 ----- >>
 ----- >>>> Backflow preventor is rated at 175 (as are most of the fire
 ----- >>>> sprinkler
 ----- >>>> components) yet we are required to do a 200 psi
 ----- >test. Is the keyword
 ----- >>> here
 ----- >>>> "working pressure" of 175 psi or am I missing something?
 ----- >>
 ----- >>>> thx,
 ----- >>>> _______________________________________________
 ----- >>>> Sprinklerforum mailing list
 ----- >>>> [email protected]
 ----- >>>>
 ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 ----- >>
 ----- >>>> To Unsubscribe, send an email
 ----- >>> to:[EMAIL PROTECTED]
 ----- >>>> (Put the word unsubscribe in the subject field)
 ----- >>
 ----- >>
 ----- >>
 ----- >>_______________________________________________
 ----- >> Sprinklerforum mailing list
 ----- >> [email protected]
 ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 ----- >>
 ----- >> To Unsubscribe, send an email
 ----- >> to:[EMAIL PROTECTED]
 ----- >> (Put the word unsubscribe in the subject field)
 ----- >>_______________________________________________
 ----- >> Sprinklerforum mailing list
 ----- >> [email protected]
 ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 ----- >>
 ----- >> To Unsubscribe, send an email
 ----- >> to:[EMAIL PROTECTED]
 ----- >> (Put the word unsubscribe in the subject field)
 ----- >>
 ----- >>_______________________________________________
 ----- >> Sprinklerforum mailing list
 ----- >> [email protected]
 ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 ----- >>
 ----- >> To Unsubscribe, send an email
 ----- >> to:[EMAIL PROTECTED]
 ----- >> (Put the word unsubscribe in the subject field)
 ----- >>
 ----- >>
 ----- >_______________________________________________
 ----- >Sprinklerforum mailing list
 ----- >[email protected]
 ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 ----- >
 ----- >To Unsubscribe, send an email
 ----- >to:[EMAIL PROTECTED]
 ----- >(Put the word unsubscribe in the subject field)
 
 _______________________________________________
 Sprinklerforum mailing list
 [email protected]
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
 
 To Unsubscribe, send an email to:[EMAIL PROTECTED]