Dave
In every instance we have to do a 3 head calc when there are at least 3
heads in the room where the steep pitched roof is (over 8:12).  We've also
had to use the UL listed flow required for the head up to 8:12 pitched
ceilings which is 18gpm per head.  These homes are also usually large homes
on wells which means we have to put in 600+ gallon (10 minutes X 54gpm = 540
gallons) tank and a pump.  The AHJ's want a cushion just in case the pump is
pumping more than the required 54gpm and draining the tank too fast.

Herb Schairbaum
Blue Water Fire Sprinklers
253-279-3603
253-927-8781 Fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of David Killey
Sent: Thursday, June 12, 2008 2:41 PM
To: [email protected]
Subject: Residential sprinklers in sloped ceiling over 8/12 pitch


It is my understanding that there are still no residential sprinklers
approved for installation in sloped ceiling greater than 8/12 pitch. This
leaves it up to the local AHJ which has resulted in a few different
requirements.
I would like to hear from anyone who may hold the solution to this on going
dilemma. What does your AHJ required you to do in these situations??
Any help would be greatly appreciated.



Thanks
Dave Killey
Fire Busters Inc

No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.524 / Virus Database: 270.3.0/1498 - Release Date: 6/11/2008
7:13 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to