PS. Forgot to add.... there are two standpipes (one in each stairwell)
supplied by common feed at the bottom.




On 6/16/08, IPA <[EMAIL PROTECTED]> wrote:
>
> I've got a dedicated pump feeding a Class II Standpipe system w/ 1 1/2"
> hose stations. I need some clarification on how many stations to calc.
>
> From reading NFPA #14 my first guess would be (2) one at each
> standpipe. NFPA #14 7.10.2.2.1  reads, "Hydraulic calculations and pipe
> sizes for *each* standpipe shall be based on providing 100 gpm..." But
> 7.10.2.1.2  states, "Additional flow shall not be required where more than
> one hose connection is provided."
>
> ...and then there is 7.10.2.2.2,  "Common supply piping serving multiple
> standpipes shall be calculated and sized to provide 100 gpm (379 L/min)."
> How does this fit into the scenario?
>
> Thanks,
>
>
>