Yes they are sampling ports. "A" in also known as the interface, which is
where the water meets the antifreeze. (Should always test as water at this
point) "B" should always test as antifreeze. "A" becomes important when
systems area higher than "A", because antifreeze is heavier than water, you
want to keep it below "A"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Loren Johnson
Sent: Wednesday, June 18, 2008 8:23 AM
To: Sprinkler Forum
Subject: ANTIFREEZE PIPING ARRANGEMENT

Dear AFSA Forumites:

We're designing fire sprinkler protection for a new CVS store and we have a
small 2 head antifreeze system to be installed. In looking at Figure 7.6.3.1
in the 2007 edition of NFPA 13, can anyone tell me the purpose of the two
valves marked as "A" and "B"?  Are they testing and sampling valves, and do
they need to be listed for fire protection service as well?

Thank you.


Loren Johnson
The Hitchcock Company
Peoria, IL


      