16.1.4.1 Where sprinkler protection of building columns within the rack
structure or vertical
rack members supporting the building are installed in lieu of fireproofing,
sprinkler protection
in accordance with one of the following shall be provided:

(1) Sidewall sprinklers at the 15 ft elevation, pointed toward one side of
the steel
Column

(2) Provision of ceiling sprinkler density for a minimum of 2000 ft2 with
ordinary
165_F or high-temperature 286_F rated sprinklers as shown in Table
16.1.4.1 for storage heights above 15 ft , up to and including 20 ft

TABLE 16.1.4.1 Ceiling Sprinkler Densities for Protection of Steel Building
Columns
Aisle Width
4 ft (1.2 m) 8 ft (2.4 m)
Commodity
Classification gpm/ft2 (L/min)/m2 gpm/ft2 (L/min)/m2
Class I 0.37 
Class II 0.44 
Class III 0.49 
Class IV and Plastics 0.68 

I am questioning option 2, it this saying if my overhead system is greater
than the density and remote area size and 20 ft. or less in storage I do not
need column protection?