Bill, I do not see the definition that way. I think you are reading into it
to much. The Pipes supplying sprinklerS, either directly, or Through..
Sprigs, drops, etc.... It is making a distinction in the different ones,
further clarified by the definitions for sprig, drop, armover., etc..

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Thursday, June 19, 2008 7:57 AM
----- >To: [email protected]
----- >Subject: RE: Restraint of Branch Lines
----- >
----- >A branch line can be a single head per the definition in 
----- >NFPA 13.  Does this mean each arm-over, drop, or return 
----- >bend regardless of length must have a branch line 
----- >restraint?  It seems sprigs are given special attention 
----- >in Chapter 9 but the other categories of branch line are not.
----- >
----- >I guess I'm getting back to the confusion over the 
----- >definition of a branch line.  From the feedback it seems 
----- >no one is providing restraint when a single head is involved.
----- >
----- >Bill Brooks
----- >
----- >William N. Brooks, P.E.
----- >Brooks Fire Protection Engineering Inc.
----- >372 Wilett Drive
----- >Severna Park, MD 21146
----- >410-544-3620 Phone
----- >410-544-3032 FAX
----- >412-400-6528 Cell
----- >
----- >-------- Original Message --------
----- >Subject: RE: Restraint of Branch Lines
----- >From: "Thom McMahon" <[EMAIL PROTECTED]>
----- >Date: Wed, June 18, 2008 4:50 pm
----- >To: <[email protected]>
----- >
----- >13 defines restraint as a lesser level of control than 
----- >Brace. We have always favored the 12Ga. 440 Lb. Ceiling 
----- >wire restraint on the end of branchlines (9.3.6.1 end 
----- >Head) If it doesn't have heads on it, it is a feed or 
----- >cross main and requires bracing. (See branchlines over 
----- >2")(This includes all head types, SSU, SSP and HSW even 
----- >flex heads if the last head on the line is a flex head) 
----- >The new 2007 hanger with 2nd hanger at 45' angle may 
----- >appeal to some. In any case when you're doing seismic 
----- >the end of branchlines must be restrained.(I always try 
----- >to keep my hangers less than 6" and it's a lot
----- >easier.)
----- >
----- >The more difficult restraint requirement A9.3.6.4 is 
----- >when your close to other objects that can damage the 
----- >branchline in a seismic event.
----- >Components of the structure, duct work or large 
----- >mechanical piping. Also your always required to use 
----- >restraint per 9.3.6.4 (see table) on longer branchlines. 
----- >Again a little clarification that this is not 
----- >cumulative, it is based upon the smallest pipe size in 
----- >the branchline.(13 HB committee, yes or No?) (Part of 
----- >this answer depends upon weather the other trades are 
----- >providing seismic bracing, and a good feel for how close 
----- >is too close, NOT YET DEFINED BY 13)
----- >
----- >Example:( A branchline which follows pipe schedule sizes 
----- >with every head 12' from the last with a 21/2" starter 
----- >piece, and 10 heads total.
----- >(112'-0" total length) you have your end restraint, the 
----- >with a Cp 0.58 you space your next restraint 38' from 
----- >the end one. Then since your now on a 11/2" piece of the 
----- >branch line do you space 38' again or 43'? The end 
----- >answer is it doesn't really matter, you need the end on 
----- >plus two more either way, but I see both sides of that, 
----- >and it's not real clear.)
----- >
----- >Thom McMahon, SET
----- >Firetech, Inc.
----- >2560 Copper Ridge Dr
----- >P.O. Box 882136
----- >Steamboat Springs, CO 80488
----- >Tel: 970-879-7952
----- >Fax: 970-879-7926
----- >
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, June 18, 2008 12:54 PM
----- >To: [email protected]
----- >Subject: Restraint of Branch Lines
----- >
----- >2007, 9.3.6.3 - The end sprinkler on a line shall be 
----- >restrained against excessive vertical and lateral movement.
----- >
----- >1. Can I assume the word line means "branch line" based 
----- >on the title of 9.3.6?
----- >2. Would the end sprinkler include sprinklers on drops, 
----- >arm-overs, and return bends?
----- >3. Would "excessive" be defined as using a restraint not 
----- >listed for vertical and/or lateral movement or not 
----- >meeting 9.3.6.1(5)?
----- >
----- >Someone has asked me to approve a particular brace but 
----- >then I realized I had no idea how many needed to be installed!
----- >
----- >(Getting old but still learning)
----- >
----- >Bill Brooks
----- >
----- >William N. Brooks, P.E.
----- >Brooks Fire Protection Engineering Inc.
----- >372 Wilett Drive
----- >Severna Park, MD 21146
----- >410-544-3620 Phone
----- >410-544-3032 FAX
----- >412-400-6528 Cell
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to