It is in the stair.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dyce
Geoffrey H.
Sent: Thursday, July 24, 2008 11:17 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

Where is the standpipe located?  It cant be in the stairwell!

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, July 24, 2008 1:34 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

Yep, we are putting valves on the floor landing for one half of the
scissor stair and valves on the intermediate landings for the other
half.

Thanks to everyone that contributed, as usual it has been quite
educational.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, July 24, 2008 8:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

Apples and Oranges.

The IBC Chapter 10 issue is means of egress, and accordingly separation
of same (remoteness). Since scissor stairs don't satisfy the remoteness
test they in the context of  Chapter 10 (1015) are considered one
stairway.

The IBC Chapter 9 issue is fire suppression, and accordingly requires
that Class I hose connections be provided in all of the following
locations;
"In every required stairway". Within the context of Chapter 9 (905.4)
scissor stairs are two stairways.

John Drucker
Fire Protection Subcode Official (AHJ)
Red Bank, New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Thursday, July 24, 2008 11:17 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

More confusion.   Back to Steve K.'s point about it only counting as one
stair (thanks for that, BTW), I still think that you have to provide a
complement of Class I connections on BOTH sets of landings.  Even if a
scissor is only considered one stair, it's most certainly a required
exit stair and if you can't guarantee the fire fighter ingress route, I
think you have to account for either or both sides of the scissor being
used.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dyce
Geoffrey H.
Sent: Thursday, July 24, 2008 5:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

That is correct Steve, at least here in Florida.  However, we cannot run
the standpipe within the stairwell as we penetrate alternating fire
levels with the standpipe.  Here, we need permission from the fire
marshal to do that.
Geoff Dyce

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, July 23, 2008 6:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement

Don't know if there's an official moniker, but we call it a scissor
stair and it's an architectural device that satisfies at least two of
your required exits and gets a LOT of your occupant load out of the
building in a relatively smaller (and localized) footprint area.   The
code requires that standpipe connections be located at either the
intermediate or floor level landings of every required exit stair so I
believe it is correct to put a standpipe connection at the landings of
EACH stair (i.e. two per level within the shaft) because you have two
stairs.

Steve Leyton
Protection Design & Consulting

The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:32 PM
To: sprinklerforum@firesprinkler.org
Subject: Standpipe/Stair arrangement

This is a tough one to put into words, drawings would better explain.

We have a stair tower (one of three) in a hotel that has two
entrance/exits on the first through fourth floors and one door on the
other 27 floors. There is no dividing wall between the stairs. Imagine
two people enter through separate doors on the first floor and as they
head up the stairs they pass each other halfway up to the intermediate
landings. You could actually climb over the railings from one stair to
the other.

We have installed a single standpipe through the floor landings on
floors 5-27 and continued to the first floor. Now the AHJ is thinking we
need a hose valve adjacent to the other entrance on floors 1-4. Both
doors access the same fire area.

I hope y'all can decipher.

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to