Bryan,
I asked NFPA about this same issue and was told that it only applies to
pendants and uprights.  
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bryan
Dann
Sent: Friday, July 25, 2008 12:35 PM
To: [email protected]
Subject: Ceiling Pockets

 in NFPA 13, 2002
8.6.7 Ceiling pockets
Does this section only pertain to pendent and uprights?
I have a situation where sidewalls are used under a flat ceiling with a
ceiling pocket less than 500 ft3 off to one side.

Thanks for any input.