I'm looking forward to the day when all the gauges are digital and we
won't have to guess if the pitot pressure from the 4" hydrant butt is
28.4 or 28.8 (lmao). It could be critical if your local sprinkler
scientist won't let you slide on 31 gpm.

Happy Friday everyone,

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, August 01, 2008 8:59 AM
To: [email protected]
Subject: RE: Gauge Calibration

RE-testing a fire pump for not using calibrated gauges, is an AHJ issue.
Calibration is only required once a year as far as I can see, for any
testing device. By doing that it doesn't mean that your gauges are
correct or in spec.(it means they were when they were tested.) Just as
with BFP you can test and pass a device, and then disconnect and
re-connect your gauge, and it will fail. Was the first test wrong or a
failure? NO. At the time of the test it passed. Does that indicate or
mean anything about any other time? NO. Calibration for Fire protection
is more Just A "Warm Fuzzy"
than
an indication of the exacting science of our profession. As you said on
a fire pump test your matching a pre-determined curve, any large
variation would alert you to an issue such as a bad gauge.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
(forum)
Sent: Thursday, July 31, 2008 8:20 PM
To: [email protected]
Subject: RE: Gauge Calibration

Tom,

Fortunately it was a small pump and the gauge in question was the one
used on the single hose monster. Fortunate our pump rep. had one in his
van with the calibration paperwork.

Why would I need to re-test when the calibration is not required by NFPA
20 (03)?

Ken

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, July 31, 2008 6:12 PM
To: [email protected]
Subject: RE: Water Supply

Ken if you're doing BFP testing you get your test sets calibrated each
year, you can send your gauges in at the same time. Personally we keep
two sets and that way we are never without one as they expire one month
apart.
 Additionally if you run into this problem at test, I would offer to run
the test, then insert the gauge in an envelope addressed to the
calibration co, record the serial # of the gauge. (If it doesn't have
one write one on it in marker. Note that # on the test report. Offer to
let the AHJ stick it in the mail, and include a request that the AHJ be
copied on the Calibration report. When it comes back, if it's within 1%
your test is complete, if not you may have to re-test, which it sounds
like you have to do anyway.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
(forum)
Sent: Thursday, July 31, 2008 2:41 PM
To: [email protected]
Subject: RE: Water Supply

Ok guys and gals.....here's one for ya.

Just did a pump acceptance test under 2003 edition of NFPA 20. The
inspector shows up on site and asks for calibrated gauges. Even though
we pulled out a gauge that came from the factory 3 months ago, he wanted
to see the paperwork. (I guess he didn't like the dirt that was on the
gauge either from a previous diesel pump flow test. Turns out things get
muddy when you do those) After reviewing NFPA 20 (03) I see that there
is not a requirement for gauge calibration except in the appendix, to
which no tolerance for the gauges is given. 

I questioned the inspector on the requirement and asked for a code
reference. What I got back was the re-write that appears in the 2007
edition of the acceptance procedure that does note that gauges must be
calibrated and within +/- 1%. I'm fine with that, except for the fact
that here in Pennsyltucky and in his jurisdiction, the 2003 is the
applicable standard.

Now to take it one step further, the new NFPA 20 (07) mentions that the
gauges must be calibrated annually (depending on use...kinda open ended
don't ya think?). In speaking with some folks that supplied our shiny 4
1/2"
Glycerine filled gauges, they mentioned that we could get them
calibrated, but "what are you gonna do, get them calibrated after every
use?" They do mention in the literature for our gauges (that I sent to
the AHJ) that they are calibrated at the factory. Keeping in mind that
scientists are probably using their "top of the line" gauges to measure
the force of an atom bouncing of a cow's butt.

I mentioned to the AHJ that in the meantime (till the 2007 ed comes
around), the township could purchase a calibrated gauge and use that as
a benchmark and throw the contractor's gauge(s) on a static point of the
system if they think something was tampered with.

I would be curious to see how others would handle this. AHJs especially.
You'ins keep my life interesting.

Getting calibrated gauge paperwork isn't a big deal (well it is if they
spring this on you at the time of test), but trying to enforce rules
that haven't been adopted yet kinda crosses the line in my book.

By the way, I did check out NFPA 291 (forgot the edition), there was
mention of calibration, but no mention of tolerance.

I have a headache from bouncing my head off the soapbox.

Ken Holsopple
Design Manager & Gauge Calibration Coordinator Rowe Sprinkler Systems 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.10/1584 - Release Date:
7/31/2008
12:00 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.10/1585 - Release Date:
8/1/2008
6:39 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to