What is the AHJ's definition of this space?  Is it a room or an equipment 
enclosure?

If it's an equipment enclosure, then the min. door hgt. would have no bearing.

You also then have to look at the requirement of sprinklers within an equipment 
enclosure versus in an occupied room.









Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Marshall Stout
Sent: Monday, August 25, 2008 7:49 PM
To: [email protected]
Subject: Computer room Racks with Blade Servers

I have a computer room with 3 lines of racks. Each rack line is approximately 9 
feet long and 3 feet wide. There is a 3 feet wide aisle between each rack line 
(2 aisles). Each rack is approximately 6 feet in height. Over each aisles, 
there is a lexan cover at 6-1/2 feet in height above the floor and a door at 
either end of the aisle, making a "room" 15 feet long and 9 feet wide in the 
computer room. This is for rack air conditioning. The computer room has a 
wet-pipe sprinkler system.
1. According to NFPA 101, the minimum headroom is 7 feet 6 inches. With the 
door access, would this "room" be required to have a 7 feet 6 inches ceiling?
2. To prevent sprinkler obstructions, would sprinklers be required in the 
"room"?
Your opinions will be helpful.

Marshall Stout, P.E.
Fire Protection Engineer
Redstone Arsenal, AL


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to