Thom,

There is no question in my mind that you are correct on both issues
here. I do have a 2007 13D & 13R handbook just so you know that these
are available. Annex-"6.8.2 It is only the intent of NFPA 13R to
reference the sprinkler discharge (flow and peressure), number of design
sprinklers, and position of sprinklers (distance from walls, ceilings,
and other sprinklers) requirements of NFPA 13. Other rules from NFPA 13
such as sprinklering of combustible concealed spaces, hose stream
demand, and water supply duration are not intended to be referenced by
6.8.2 to apply to those systems or portions of systems that are outside
the dwelling unit but have been determined to be considered residntial
orincidental to residential and within the scope of this standard." I
believe that this is saying just what you are.

Rod DiBona
Vice President
Rapid Fire Protection
605-348-8914 ph
605-348-0108 fax 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, August 27, 2008 11:59 AM
To: [email protected]
Subject: RE: NFPA 13R Areas of 13 protection

Does anyone have a 13R handbook (I heard last year they were thinking of
doing one, but haven't seen anything yet.)

Question has arisen about the meaning of 6.8.2 Design Criteria outside
of the dwelling unit. Short version "Protect as per 13." AHJ says that
means protect the pool area using 3000 SF design area @ 0.10 and (Here's
where we differ seriously) Protect the attic wood truss space above.
I believe the intent is that the spaces that would be exempt from
sprinkler protection in 13R remain exempt, and only those areas which
don't fit the residential requirements of 13R must be protected by as if
you were applying 13. So attics, crawl spaces and concealed combustible
spaces remain unprotected.
Is this how you all see it. (I even question the 3000 SF requirement,
because the spaces that drive the 3000 are outside the scope of 13R, and
therefore should not affect the areas of 13R that require 13
protection.)

Any ideas or comments appreciated.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to