Until you're sloshing around in a room that has had a two inch
discharge running for 45 minutes and then he's blaming the sprinkler
system when it was crap in the water purveyor's water that clogged the
little by-pass hose that supplies pressure to keep the RP closed and
wouldn't have clogged in the first place if the water wasn't moving
constantly because the RPBA was there in the first place or if the
owner had sprung for a strainer or if the purveyor cared as much that
his pipes were flushed properly after an opening as he does that the
backflow is installed.

On Wed, Aug 27, 2008 at 5:34 PM, Garth W. Warren <[EMAIL PROTECTED]> wrote:
> Thom - I love your reasoning and your solution.  I agree backflow rooms
> should have drains to properly remove discharge waters but from everything I
> have seen the codes only specify drainage capacity on below-grade RPZ
> installations.  Some AHJs in this area refuse to specify proper types let
> alone proper installations - more from a lack of knowledge than from being
> unreasonable (I think), but when it is brought to their attention they
> refuse correction or future compliance.....  Some simply state they do not
> refuse or approve backflows that is the water supers job...  They are the
> AHsomeJ.
> I am in the north where outside installations with hot-boxes are rare.
> Curbs and scuppers or drains such as you suggest should be a requirement on
> all in-building RPZ installations.  Until it is code - all that can be done
> is warn of the possibility of disaster, which I personally have not found to
> be very effective with cost conscious builders and owners.
>
> Garth
>
> ----- Original Message -----
> From: "Thom McMahon" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Tuesday, August 26, 2008 11:14 AM
> Subject: RE: backflow preventer drains
>
>
>> Garth:
>>
>> I'm not saying that a drain would be required on an "Outside"
> installation,
>> as we see on vacation to those warmer climates. We're talking
> installations
>> inside of buildings. The IPC says a "Riser room" is a mechanical room, and
>> requires a min. 2" drain in all mech rooms. Double check or RPZ the room
>> will have a floor drain of 2" or it may be installed in a freely draining
>> area or words to that effect.(So if it's in a room it's a mech. room and
>> must have a drain, if it's in a warehouse or other open area it must be
>> freely draining.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to