Based on UK insurers protocols any FM200 protected space is unsafe for occupation at such concentration levels. Most companies follow similar procedures for CO2 systems and evacuate FM200 protected rooms before the gas is discharged.

Stewart


On 3 Sep 2008, at 19:05, Reza Esmaeili wrote:

Thom,
What makes me worry is that we say FM-200 gas is safe for occupied spaces & will not affect the personnels in the computer room. Imagin that the volume of cabinets is about 25% of total volume, so if my design concentration is 7.4% then the real concentration is 9.25%. I agree that cabinets are not "Gas Tight" and will become filled with the FM200 just at a slower rate, but it takes time, may be for 2 minutes, then can we still say this gas is safe while the personnels may be subjected to 9.62% even at the first 2 minutes of gas release?

Thanks,
Reza



Short answer NO!

The cabinets are not "Gas Tight" and will become filled with the FM200 just
at a slower rate, than the rest of the room.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to