Todd. I did a test the other day. The water purveyor insisted that we shut one of the control valves on the loop and test the hydrant furthest downsteam. The gauge hydrant was upsteam ofc the test hydrant. The purveyor insisted that the loop should not be fully open. Is that corect? We were getting infp for a future system. Sent from my Verizon Wireless BlackBerry
-----Original Message----- From: Todd Williams - FPDC <[EMAIL PROTECTED]> Date: Tue, 23 Sep 2008 10:38:39 To: <[email protected]> Subject: Re: Flow Hydrant vs. Test Hydrant The way that I have always done it was to try to get the effective point of the test as close to the building as possible. The effective point is the junction of flowing and non-flowing water. Often is turns out to be the intersection of the hydrant spur with the main line. There could be exceptions depending on the arrangement of the hydrants and the lead in, but that would need to be looked at individually. At 10:12 AM 9/23/2008, you wrote: >Content-Type: text/plain; > charset="us-ascii" >Content-Transfer-Encoding: 7bit >Content-Disposition: > >O.K., can someone please help a dummy out (that would be me)? When looking >at a Civil Site Utility plan what method do you use to determine which >hydrant you want to flow and which one you put the gauge on? I've heard a >couple different ways, just wanted to get a popular opinion > > >Regards, > > ><http://www.firstdefensefire.com/> > > > > > > > > >E-mail message checked by Spyware Doctor (6.0.0.383) >Database version: 5.10760 >http://www.pctools.com/en/spyware-doctor-antivirus/ > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [EMAIL PROTECTED] > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
_______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)