When using low pressure dry systems, one needs to change the train of thought 
when comparing to conventional dry pipe systems.  The range between the nominal 
operating pressure, the low air pressure signal and the trip pressure are very 
tight, and you do not have the air pressure "cushion" that is normally provided 
with conventional dry pipe system air pressure ranges.   Therefore, using a 
regulating type of air maintenance device and a tank-mounted air compressor or 
owner's air with low pressure dry systems is the best combination to prevent 
any mishaps.  Using this configuration provides the system with a constant air 
pressure value, and the capability for safeguarding against minor air loss or 
rapid changes in air pressure, of which both accelerators and pressure 
actuators are sensitive to.  Controlling-type air maintenance devices used in 
conjunction with bare (non-automatic) air compressors do not have this 
capability.  Additionally, when manifolding air supplies for such systems, each 
system riser should hve its own regulating type of air maintenance device.

Regards,

Salvatore Izzo, P.E.
Manager - Reliable Technical Services
________________________________________
From: [EMAIL PROTECTED] [EMAIL PROTECTED] On Behalf Of Fox Duane T. 
(FireMarshal) [EMAIL PROTECTED]
Sent: Wednesday, September 24, 2008 8:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry Valve Keeps Tripping

Brian,

   You need to read the Victaulic fine print.  We had the same problem
in Delaware.  You need an air maintenance device.  It seems that they do
not "require" the device but do recommend it.  Apparently the diaphragm
is very sensitive and will false trip with air surges.  As I stated we
had several issues with different installers, so we started checking
into it, having the Victaulic rep do an informal class for the FMO.
When we asked why the maintenance device is not required by the
manufacture the rep stated competitive cost.  All the problems we had
were solved by installing an air compressor with a tank and an air
maintenance device.

Duane T. Fox, Jr.
Asst Chief, Technical Services
DE State Fire Marshal's Office

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Wednesday, September 24, 2008 8:25 AM
To: sprinklerforum@firesprinkler.org
Subject: Dry Valve Keeps Tripping

The valve originally was tripping within a couple of days, then it held
for
3-4 months, then it began to trip again, sometimes within 2 hours after
setup, the entire valve assembly was replaced, the system held for 3-4
days
and now has tripped again. FYI, Victaulic NXT Dry Pipe Valve pre-piped
version is being used. Also, the system was introduced with debris due
to
false underground papers provided, however the system was flushed
thoroughly, can there be any residual problems from this? Can the air
compressor have any impacts, even though the dry valve is one of those
low
air pressure valves? This installation is at a Hospice and the Fire
Marshal
will not let the strobes be turned off until the system is put back into
service. the owner is hot, to say the least!



Regards,


<http://www.firstdefensefire.com/>








E-mail message checked by Spyware Doctor (6.0.0.383)
Database version: 5.10770
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to