And nobody thinks that might be a problem? I have installed these heads
four feet below a ceiling and outside with only the mullion to act as a
heat collector. Seems like quite a leap of faith to assume the sprinkler
will activate in a timely manner.

Ron Fletcher



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, October 01, 2008 8:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

Yes.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, October 01, 2008 8:10 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

So the test assumes the glass remains intact until sprinkler activation?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, October 01, 2008 7:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

The window sprinkler was tested using the exact same criteria as is used
to establish any other rated assembly.   A test fire is built on one
side of the subject and burned for the duration of the rating and then
there's a steady-stream hose test (not entirely sure if that's of the
same duration - Drucker, chime in now please) during which water is
jetted against the subject and it can't fail.  I think your assumption
is correct that the surface is protected so long as the sprinkler(s)
flow at their minimum required rate - 15 or 20 GPM depending on spacing.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, October 01, 2008 6:43 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

Just a guess but I think the window damage (without the sprinkler
protection) would occur within the first minutes.  Once the minimum
water discharge is established I would assume the protection would last
as long as the water is flowing.  Does this sound logical?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: Window Sprinklers
From: "Bill Minkel" <[EMAIL PROTECTED]>
Date: Wed, October 01, 2008 9:27 am
To: <sprinklerforum@firesprinkler.org>

Ahhhhh, Gotcha

Bill Minkel, Designer
Dallas, TX
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, September 30, 2008 3:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

Of course it's MORE than adequate for a 1 hr wall, the question was is
there
a "Less" that would work for 1 hr, but not 2 hr? Maybe a smaller orifice
or
totally different head or even a vert. sidewall? Hence "Window Sprinkler
Lite"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Tuesday, September 30, 2008 11:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

Educate me here, I would have thought that a wall assembly rated for 2
hours
would also be more than adequate for 1 hour?

Bill Minkel,

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to