The article I read said that there is static pressure inside the short
tube that contains the pitot inlet. The static pressure adds to the
velocity pressure to give an artificially high gauge reading. This would
back up your findings that the hose monster indicated less flow than the
diffuser.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ   

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Wednesday, October 15, 2008 6:39 AM
To: [email protected]
Subject: RE: FLOW / PITOT READINGS

I bought one years ago for a project I bid on ISO testing a town north
of
Boston (Bahstin).
They required it to be used in the contact.
Once a year or so later I was using it and the underwriter was present
and
he wanted more water (wata) flowed.
I only had one so I got a monster and hose and flowed another hydrant,
much
less water from two.
He questioned the diffuser so we took it off and put on a monster and 10
foot hose and opened it.  Less than the diffuser.
I know the monster was working right as I had checked it against a
playpipe
and flow meter and it had a calibrated gauge.
>From that time on, I shelved the diffuser and never used it again.
Same
with that in-line 2.5"  rig they have, gathering dust.
My take is it's too close to the opening, not a diameter away and right
where the nozzle begins to flare out plus that cheap gpm/psi plastic
gauge
bounces and I don't know how accurate it is either.  I've seen too many
instances of bad data used in sizing pumps and what problems that brings
and
can only imagine what issues it could bring so a simple sprinkler design
and
nobody would know.  It's like building on a cracked foundation imho.
Sorry
to pontificate, strong coffee today.  :)
FGOL



Tom,

Do you know why the Pollards are in accurate? I have read that there is
problem with the pitot being inside a short tube.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to