And when you put water on the Haz Mat chemicals what do you end up with? How is the resulting liquid Haz Mat going to be dealt with? Dykes, underground tanks, just let it run into the storm drains, hope it evaporates?

Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc


----- Original Message ----- From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, October 16, 2008 12:34 PM
Subject: RE: Pesticides Storage


Ray,

First in order to do any kind of analysis you need MSDS on ALL of the products to be stored, then you need to know what kind of conatiners, if they are racked or palletized, how high and how much. Do you have a rack or storage arrangement plan? I assume you already know the building construction characteristics?

Don't assume that NFPA 30 will be the only place to look. Flammables and combustible liquids will probably be the least of any commodity when it comes to pesticides. Mostly you'll be dealing with toxics and highly toxics which don't have a big impact on the fire protection systems in and of themselves but they do have major impact on other systems which could in turn affect your installation, such as ductwork (obstructions). Toxics are addressed in the Building Code as far as allowable quantities in reference to occupancy classifications. Most likely you will be dealing with an "H" Occupancy.




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to