Not that it impacts the issue of water supply adequacy, but the current Class 
III (and II) standpipes are now described as "for use by trained personnel" and 
not occupants.   I commend the query, especially on behalf of an HOA, but I 
would contact the serving fire department about how to proceed and what 
obligations there are under local laws and code WRT to retroactively upgrading 
the water supply.   Was it inadequate to begin with, or degraded over time?  
Under what code was it originally installed, etc., etc.    
 
More importantly, is it connected to an FDC?  Most fire departments will NOT 
use those hoses if they access the valves, but if there's no FDC they won't use 
them at all.   I recommend using this opportunity to partner with the FD to 
make the standpipe system more responder-friendly and perhaps saving $$ by 
re-working the FDC instead of upgrading the water supply.
 
Steve Leyton
Protection Design & Consulting

________________________________

From: [EMAIL PROTECTED] on behalf of Mark Hasenmyer
Sent: Fri 10/31/2008 6:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Building fails pressure test



The Class III is for occupant use; therefore adequate pressure must be
present at all times.  The Class I is for FD use and they bring the pressure
with them (fire truck).  Therefore with Class I it doesn't matter if the
water supply can meet the demand; it becomes a manual standpipe. 

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete Laszcz
Sent: Thursday, October 30, 2008 10:46 PM
To: sprinklerforum@firesprinkler.org
Subject: Building fails pressure test

I am the HOA president for a 4 story condominium that has a Class III
standpipe system installed.   The building was only required to have a Class
I dry standpipe installed but for reasons not clear, we have a class III
system installed.   Our building can only produce 25 PSI at 375GPM on the
roof instead of the 100 psi per our fire department (their email below).
They say that we could remove the class III and install a class I and not
worry about pressure.  This seems unnecessary as a lower pressure class III
must be equal or superior to a Class I dry standpipe.  We are in California
in a city with a full fire department. 



Any suggestions as to how to proceed?



Thanks



EMAIL FROM FIRE DEPARTMENT





"When the building was constructed it was required to have a "Type I
Standpipe installed" according to the 2001 Uniform Fire Code (the edition
used when this structure was built).  The owner at the time opted to install
a Class III Standpipe System, which is an approved system.  According to
NFPA 14, section 7.8.1 the "minimum residual pressure of 100 at the outlet
of the hydraulically most remote 2 ½ inch."  This pressure is reduced to 65
psi only when the outlet is 1 ½ inch which this system is not. 



The XXXX  cannot arbitrarily circumvent the fire code in lieu of safety
standards.  We have researched two viable options that will remedy the
situation and still be code compliant.  They are as follows:



1.       Provide a vertical booster pump to supplement the loss of pressure
in the sprinkler/standpipe riser.



2.       Install a Class I Standpipe (Dry Pipe), which is required by the
2001 CFC for this occupancy type.  This action would require submittal of
plans for review, change from a Class III to a Class I Standpipe, and the
addition of fire department connections.  "







_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to