NFPA-25 only applies to ITM, NFPA-20 applies to initial design and
acceptance. 

In that regard; 2007 NFPA-20 14.2.7.2.2 applies to Field Acceptance Test
Procedures, the testing provisions don't justify nor negate the general
requirements. Preceding 14.2.7.2.2 of the standard is  5.14.3.1, 3.2 &
3.3, the general requirements, specifically the sizing of suction
piping.  

Keep in mind that 14.2.7.2.2 was not intended to do away with the 150%
flow requirement and the piping sizing requirements but rather to
address situations where the available water supply such as a city water
main was capable of delivering system demand but incapable of delivering
150%. Even if the available water supply is incapable of 150% delivery
according to the standard the suction piping must sized to do so.

Frankly it's a design issue. A properly sized pump is available and
would satisfy the requirements of the standard.

Sincerely,
John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, November 07, 2008 10:18 AM
To: [email protected]
Subject: Re: Fire Pump Suction

NFPA 25 2008,  8.3.3.1.1 If the available suction supplies do not allow
flowing of the pump at 150 percent, flow at maximum.
Sent from my BlackBerry Smartphone provided by Alltel

-----Original Message-----
From: "Fletcher, Ron" <[EMAIL PROTECTED]>

Date: Fri, 7 Nov 2008 07:35:48
To: <[email protected]>
Subject: RE: Fire Pump Suction


What's the problem? Test the pump at 100% capacity and quit.

14.2.7.2.2 If available suction supplies do not permit the flowing of
150 percent of rated pump capacity, the fire pump shall be operated at
maximum allowable discharge to determine its acceptance. This reduced
capacity shall constitute an acceptable test, provided that the pump
discharge exceeds the fire protection system design flow and pressure
requirements.

Ron Fletcher
Aero Automatic
Phoenix, AZ

P.S. 
Todd, sounds like that hospital was designed for 3 manual wet standpipes
and the 250 gpm pump is there to supply the sprinkler systems.



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Friday, November 07, 2008 7:10 AM
To: [email protected]
Subject: RE: Fire Pump Suction

As the saying goes bigger is not always better. 

Sadly I hang my head when I hear where was the EoR.

John Drucker 
Fire Protection Subcode Official (AHJ)
New Jersey 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, November 07, 2008 8:19 AM
To: [email protected]
Subject: RE: Fire Pump Suction

It's nice to see that I don't get all of this stuff to figure out. I
wonder where the EoR was on this project? I also love the term "had
access". Is this a pump he mis-ordered for another job and got stuck
with?

If this were my crisis, I would run a test increasing the flow in 100
gpm increments until I got to the -3 suction. That would give me what I
can run the pump to flow wise. Assuming you hit the -3 before the 600
gpm, you essentially have three choices: install the correct pump,
change out the suction line or come up with a way to live with the
existing situation. This would probably include discussions with the
owner, pump rep and the AHJ. Best of luck.

I am working on a hospital with a 250 gpm pump that is trying to feed
3 standpipes. I'll let you know when this pump becomes available (just
kidding)





At 11:58 PM 11/6/2008, you wrote:
>The concern is the size of the suction pipe. The pump selected was 250
gpm,
>to match the 222 gpm, 40 psi demand. But the contractor had access to a
400
>gpm, 70 psi pump which got installed instead. An overkill, but that is
what
>happened. The suction piping from the tank to the pump is 4". The
engineer
>is pointing to NFPA 20, 2003 section 5.14.3.2 which requires gauge
pressure
>at pump suction flange to be no less than -3 psi. Although the flow is
not
>mentioned in this particular section, from section 5.14.3.1 it can be
>deduced that it is 150% of the rated flow. Now flowing 600 gpm through
the
>4" suction piping and avoiding cavitation is the problem.
>
>Tony
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
>Sent: November 6, 2008 1:59 PM
>To: [email protected]
>Subject: RE: Fire Pump Suction
>
>If I understand your concern you are worried the tank will run out
before 30
>minutes because of overflow due to a supply calc vs. a demand calc.
You are
>worried about calc'ed world vs. real world.  Fine but in what real
world
>will the actual design area operate.  Odds are you won't be in the
remote
>area which increases overflow meaning less than 33 minutes.  Odd are
less
>than the calc'ed number of heads will flow decreasing the demand
meaning
>more than 33 minutes.  Odds are 2 heads (or less) will flow and you
won't
>have anywhere near 222 gpm coming out.  This probability is the driving
>force showing in reality the tank will last more than 33 minutes.
>
>Overflow is good from a fire suppression standpoint anyway.  More water
per
>time equals higher probability of suppression and quicker time.  It's
also
>not linear, you get more bang for the buck with increase in density.  I
>don't know of specific figures, just going from experience.  If you put
the
>fire out in 10 minutes and the tank runs dry in 20 is there a problem?
>
>IMHO the system failed if the full remote area operates in the first
place.
>Or at least a serious investigation is warranted to determine why.  If
you
>still need the sprinklers after about 10-15 minutes there is a problem.
The
>extra heads and 30 minutes already have a deal of safety in them.
>
>The actual produced is always a balance between flow and available
pressure.
>So yes if the entire remote area opens you will in reality drain the
tank
>faster than 33 minutes.  Could be much quicker depending on the shape
of the
>pump curve and the overflow.  But assuming you are light hazard based
on the
>very little information provided I don't see a problem.  If you are
really
>curios start running system supply calc's for different areas and you
should
>see the tank will never last 33 minutes with a full sized calc'ed area
and
>much longer when less than the full area.
>
>Now maybe you are 45 minutes from the closest FD and this becomes an
>engineering question to consider. Some day the code may differentiate
>between available levels of fire service but not yet.
>
>But hey maybe I missed the point of your question.
>
>Chris Cahill, P.E.
>Fire Protection Engineer
>Sentry Fire Protection, Inc.
>
>763-658-4483
>763-658-4921 fax
>
>Email: [EMAIL PROTECTED]
>
>Mail: P.O. Box 69
>         Waverly, MN 55390
>
>Location: 4439 Hwy 12 SW
>               Waverly, MN 55390
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of
A.P.Silva
>Sent: Thursday, November 06, 2008 2:11 PM
>To: [email protected]
>Subject: RE: Fire Pump Suction
>
>The maximum sprinkler demand as per hydraulic calcs. is 222 gpm. The
water
>supply is by means of storage tanks having a total volume of 7448
gallons.
>Just barely enough for approx. 33 minimute at maximum demand. The
contractor
>has installed a 400 gpm fire pump. NFPA 20 requires gauge pressure at
the
>fire pump suction flange to be 0 psi or higher when pump is operating
at
>150% of rated flow, which in this case is 600 gpm. Is this realistic? I
>know, if the suction pressure is 0 psi or higher for 600 gpm flow, it
will
>work for all cases. However, I would expect a flow between the supply
and
>demand with all design sprinklers flowing. Anyone with experience with
>pumps, care to comment?
>
>Tony
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
>Sent: November 4, 2008 8:56 AM
>To: [email protected]
>Subject: Re: Fire Pump Suction
>
>  Boiling (cavitation) starts starts when the water pressure at the
impeller
>is reduced to the vapor pressure of water at the water temperature.
You see
>this addressed  in the pump literature as "NPSH"
>The term net positive suction pressure (NPSH) is defined as the
difference
>between the suction pressure and the vapor pressure of water and must
be a
>positive number to avoid cavitation. At 68 degrees F water temperature,
the
>vapor pressure is 0.35 psi. So, as long as the inlet pressure is
greater
>than 0.35 psi absolute or -14.3 gauge, no cavitation.
>
>In practical terms, so long as the suction pressure is above -12 to -13
psi,
>you should be fine.  When a typical centrifugal fire pump starts to
>cavitate, you'll know it. (sounds like the pump is full of rocks), and
>you're not going to damage the pump unless you let it cavitate for an
>extended period of time. The problem, of course, is that the pump
>performance deteriorates significantly.
>
>Joe
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to