Or quote NFPA 13 2002 Edition
11.2.3.2.2.1
The densities and areas provided in Figure 11.2.3.1.5 are for use only with 
spray sprinklers.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dennis Browning
Sent: Thursday, November 13, 2008 11:10 AM
To: [email protected]
Subject: Slippery Slope

I have a project we designed the Dry System with  7 SD Attic heads. The ME 
wants the Area and Slope increases per 11.2.3.2.4 and 11.2.3.2.5. I pointed out 
the listing of the Attic heads but all he says is " If it's OK with the Local 
AHJ, he takes " no exception to that design approach" but he will not stamp the 
drawings saying this, even tho he DID stamp the first set " rejected/ resubmit"!

LOcal AHJ requires plans to be stamped by the EOR or the Architect prior to 
submission, and the Architect won't stamp them " because".

Trying to build a case that what we did is " per NFPA 13 and industry standard.
Any thoughts?
Dennis Browning
Browning Fire
Medford, Oregon

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to