8.4.8.1 Special sprinklers that are intended for the protection of specific hazards or construction features shall be permitted where such devices have been evaluated and listed for performance under the following conditions:
(1) Fire tests related to the intended hazard (2) Distribution of the spray pattern with respect to wetting of floors and walls (3) Distribution of the spray pattern with respect to obstructions (4) Evaluation of the thermal sensitivity of the sprinkler (5) Performance under horizontal or sloped ceilings (6) Area of design (7) Allowable clearance to ceilings And... 1.6.1 Nothing in this standard shall be intended to restrict new technologies or alternate arrangements, provided the level of safety prescribed by this standard is not lowered. 1.6.2 Materials or devices not specifically designated by this standard shall be utilized in complete accord with all conditions, requirements, and limitations of their listings. 6.2.4.2 Special Sprinklers. Special sprinklers shall be permitted to be listed for protection of a specific construction feature in a portion of an occupancy classification. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 -----Original Message----- From: Dennis Browning [mailto:[EMAIL PROTECTED] Sent: Thursday, November 13, 2008 12:10 PM To: [email protected] Subject: Slippery Slope I have a project we designed the Dry System with 7 SD Attic heads. The ME wants the Area and Slope increases per 11.2.3.2.4 and 11.2.3.2.5. I pointed out the listing of the Attic heads but all he says is " If it's OK with the Local AHJ, he takes " no exception to that design approach" but he will not stamp the drawings saying this, even tho he DID stamp the first set " rejected/ resubmit"! LOcal AHJ requires plans to be stamped by the EOR or the Architect prior to submission, and the Architect won't stamp them " because". Trying to build a case that what we did is " per NFPA 13 and industry standard. Any thoughts? Dennis Browning Browning Fire Medford, Oregon _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)