Zebra mussels and depending on where this is located there may be other 
critters you need to be concerned about. There could also be vegetation issues.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Splawn, Shannon
Sent: Friday, November 21, 2008 8:52 AM
To: [email protected]
Subject: RE: Man made reservoir to be used for fire protection?

That was my thought and that's what I've communicated to my project manager.
But in due course of being careful with the client's money we are investigating 
all avenues.  And just to be clear - my first suggestion was the tank but it 
was conditioned on looking at this option to see the capital cost.

Looking at NFPA 25 it might be necessary to dredge the pond on a regular basis. 
What other upkeep costs are hidden by this kind of arrangement?

Shannon Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
513.674.3822
[EMAIL PROTECTED]



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Friday, November 21, 2008 8:32 AM
To: [email protected]
Subject: RE: Man made reservoir to be used for fire protection?

Sure it wouldn't be easier to install a tank?
If not, as a liner a fabritank is likely worth investigating.
Although perhaps there's a reason I've only done one fabritank in 34 years- If 
they were the answer, we'd see more of them?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Splawn, Shannon
Sent: Friday, November 21, 2008 8:04 AM
To: [email protected]
Subject: RE: Man made reservoir to be used for fire protection?

The one time that I've done something similar the pond was an existing 
condition and we just specified a pipe through the earth embanked wall and 
connected to the new pump (in summary form).

So, I guess one thing that I am looking for is: would it be cost-effective to 
bring in clean fill-dirt and build up an earth embankment on this flat ground 
so that there would be sufficient head above the pump suction intake?  What 
would be the best kind of liner to use? EPDM? Clay? Something else?

Primary source will be from a well.  I am also considering the connection to 
the public water supply as another means of filling but it has a very low flow 
rate and would be "useful" only in non-emergency conditions.  I am not taking 
any credit for replenishment of supply to reduce the size of the storage.

Thanks.

Shannon Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
513.674.3822
[EMAIL PROTECTED]



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Thursday, November 20, 2008 3:40 PM
To: [email protected]
Subject: RE: Man made reservoir to be used for fire protection?

Shannon,

What are some of the "new twists"?  Also consider sustainability.  Will it be 
reliable during drought, how is it fed, reliability of the source, potential 
evaporation rate, etc.  But it's been done many times.

Ask Jim R. about Marysville, Ohio and the Bus plant,  it had a nice size pond 
as a water source and 3 or 4 big diesel vertical turbines. That was a fun trip.



Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Splawn, Shannon
Sent: Thursday, November 20, 2008 3:14 PM
To: [email protected]
Subject: Man made reservoir to be used for fire protection?

Does anyone know of a good source of information to carry out a design that 
revolves around the idea of using a man made reservoir (a pond) for fire water 
storage?  I've done a similar design using screens and vertical fire pump a 
long time ago but this one has some new twists for me and I can't find any good 
design guidance on the subject.

Not looking for a "fabric-tank"; we are looking at a new reservoir dug 10'
feet into the ground and having a capacity of 300k to 350k gallons.  It will 
have some type of clay lining or other form of retention. The water supply 
would be piped from a nearby well.

Thanks.

Shannon Splawn, CFPS
Jacobs
Fire Protection | Mechanical Engineering Dept.
[EMAIL PROTECTED]





NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to