Joe, Try this:
NFPA 70, 2005 edition, 695.6 (F) Junction Points. "Where wire connectors are used in the fire pump circuit, the connectors shall be listed. A fire pump controller or fire pump power transfer switch, where provided, shall not be used as a junction box to supply other equipment, including a pressure maintenance (jockey) pump." Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 241 Hughes Lane St. Charles, MO 63301 636-946-0011 636-946-5172 (FAX) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Monday, December 08, 2008 10:44 AM To: [email protected] Subject: Fire Pump Controller I just had a job site meeting with a electrical contractor. He stated the engineer wanted to feed the jockey pump controller from the fire pump controller. Something about a tapping rule or exception. I cautioned against it, told him to research it first. Can anyone give me a section that prohibits this arrangement from either NFPA 20 or NEC? Best regards, Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. Phone: 406.652.7697 Fax: 406.652.7743 Cell: 406.861.4507 Email: [EMAIL PROTECTED] Web Site: http://www.burtellfire.com please don't print this e-mail unless you really need to _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)