Joe,

Try this:

NFPA 70, 2005 edition, 695.6 (F) Junction Points.  

"Where wire connectors are used in the fire pump circuit, the connectors shall 
be listed.  A fire pump controller or fire pump power transfer switch, where 
provided, shall not be used as a junction box to supply other equipment, 
including a pressure maintenance (jockey) pump."

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 10:44 AM
To: [email protected]
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to