There was a mid-rise apartment project 3 blocks east of NFPA headquarters in
Quincy that had exterior mechanical rooms with doors off the balconies and
they had a mechanical room fire about 5 years ago.  It was bad, engulfed
three levels and spread across the balconies.  Code at the time didn't
require them but I was told afterwards they were installed.  If they're not
required maybe you might want to offer it as an option.  Just a thought.

Tom Duross
FGOL


6.9.7 Sprinklers shall not be required in closets on exterior
balconies, regardless of size, as long as there are no doors or
unprotected penetrations from the closet directly into the
dwelling unit.


Thom McMahon, SET


I don't have the 13R 2007. I have the 07 handbook, which doesn't include 13D
& 13R unlike previous editions. Does 13R 2007, say anything different? 2007
is not the governing code, but I'd certainly like to know the intent.

Tony