All Dandy idea's. Now all you need to do is show that there is enough need
for this to have UL and FM develop a standard test for this installation,
then convince the MFG's that the demand for this installation is great
enough for them to spend 100's of thousands of $ to get the testing and
listing done.(If each of them tried to list just 3 HSW heads, that would be
over a million $.

Takes a lot of HSW in "Space" installations to recover that kind of
investment. Also I heard something about an economic down turn in the
economy, where money is hard to get. That could just slow things down for
several years.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Monday, January 05, 2009 2:05 PM
To: [email protected]
Subject: RE: Sidewall Sprinklers

Looking at 155°F EC pendents and uprights, 20x20 are standard response and
18x18 (or less) are quick response.  In other words, the sprinkler is either
9' away or 10' away from the fire.

This leads one to believe that it would be possible to have an exposed HSW
listed for a 10' throw for at least standard response, maybe quick response.
Note, that if a 'recessed' or even 'concealed' pendent can get a listing at
9' or 10' away from the fire, you would think an exposed sidewall 4'-6"
below the ceiling could receive a listing.  Especially since 4"-6" below the
ceiling is more ideal for a quick activation time than a recessed pendent.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487