douglas hicks

if the riser feeds a gridded system, you should not remove the pressure
relief valve.
if there is a remote inspector´s test, it is possible to suck most of the
air out of the
  system via this valve.  If this is done on a cold day, and there are no
air pockets in
  the pipe, then on a hot day, you may experience more, and more severe
leaking
  in your system.  liquid water expands, ever so slightly with temperature.
to be
  sure, so does the metal pipe, but not near as much as the water.

scot deal
excelsior fire engineering
good luck finding out if the system is gridded.  usually you have trees and
branches
in business and commercial occupancies.  It would be a safer RISK in such
circumstances,
to take the leaking valve off, in this case.

Why?  Can I just remove the pressure relief valve. My thought is the
designer specified the pressure relief valve for a reason, the valve needs
to be in place.