Well yes and noon the interlock issue but thats not really the issue at hand.  
In order to find out if FM or NFPA is going to be the standard I would consult 
the AHJ to get the perspective of the individual that says yes or no.  I have 
yet to find an AHJ that says FM will be used to substitute NFPA simply due to 
liability.  If not listed for there intended use just simply ask the AHJ to 
sign off on it then the situation is resolved.  If they will not sign off on 
that look at the deluge system.  Mines are a creature all there own and rarely 
found to resemble the next.  The main reason for this is do primarily to the 
length of the conveyor and type of material it transports.  As far as the 
interlock goes we all know how the fire tetrahedron works.  The stopping of the 
belt is not so the fire wont outrun the sprinklers it is to limit air 
flow which is fueling the fire.  The fire can only out run the sprinklers if 
the proper fuel base is
 there, so we limit the extra ingredients.  

Keep us informed.
 
Jeremy S. Blocker
 
Let us not look back in anger, nor forward in fear, but around in
awareness. --James Thurber 




________________________________
From: Rod DiBona <[email protected]>
To: [email protected]
Sent: Tuesday, February 3, 2009 8:44:28 AM
Subject: RE: Sprinkler protection below conveyors in pits

Well I have a different opinion on this Craig. Most of the time the ONLY
reason that many of these industrial sites are getting any fire
protection is because the insurer is asking for it. We have about
seventy mining sites in our working area and the majority of them have
very little or no protection at all. When the insurer is the one coming
in and ASKING the owner to sprinkler a certain hazard he is also the one
telling them how it will be done to receive the proper premium credit. I
have had several instances in the last year dealing with this exact
issue. On one of the projects where the sprinkler alone was $10 million
I adamantly asked that we cover the top and bottom belt on thousands of
feet of new belts that were being built. I showed NFPA 15 and even had a
proposal that showed that it was even more important with Powder River
Coal because of its higher propensity to spontaneous combustion. This
was a piece done by the powder river coal group. At the end of the day
the engineers said no because FM was not requiring it. Their data sheets
only require the top belt. It is one of the few times that I have seen
where the FM data sheets were clearly less restrictive than NFPA. 

Secondly most of these systems that I have seen are not deluge. This is
due to hydraulic restrictions of large deluge systems and physical
restrictions due to parallel runs of bulk needed for several deluge
systems. Most of these systems are preaction that I have seen. As you
referenced there is an interlock that shuts down the conveyor upon
activation isn't that so that the fire doesn't "out run the sprinklers."

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 03, 2009 6:56 AM
To: [email protected]
Subject: RE: Sprinkler protection below conveyors in pits

First, Unless FM's guidelines exceed NFPA I wouldn't be replacing the
NFPA standard with the FM guidelines since NFPA is usually referenced in
the building codes and FM's Data Sheets are not.  So if NFPA says do top
and bottom and FM says only do bottom I'd be doing top and bottom.

Second, Conveyor system protection is found in more detail in NFPA 15
(7.2.3, 2007) since these are almost always deluge type systems.
Definitely would not want to use closed heads in this application as the
fire could out run the sprinklers or the sprinklers may not respond at
all due to the belt movement.

A typical installation would consist of open spray nozzles usually with
a broad angle spray pattern with linear heat detection or other heat
detection method to set the system off. Manual activation is also a
common accessory to the system.

Also it wasn't stated what was being conveyed.  There are other NFPA
Standards for various industries or hazards which provide additional
information on protection of conveyors in specific applications. 

With open nozzles such as Tyco's Protectospray or Reliable's Model A or
Viking's Model E or other similar, you can select the discharge angle up
to 180 degrees,  the nozzle can be placed with a few feet of the object
you are protecting with no loss of integrity of the spray pattern.  This
is something you can not accomplish with a typical SSU or SSP.  They are
not made for this type of application.  You must determine the
appropriate spray angle as you determine the distance between the nozzle
and the belt (axial distance).  As you get closer to the belt naturally
the spray pattern area will get smaller.  Also understand that you have
various K-factors to choose from.  Choose the correct K-factor nozzle to
deliver the needed amount of water to the hazard.  You do not need to
use just 5.6K's everywhere.  If this is an enclosed conveyor make sure
the structural people as well as the conveyor mfgr. know about how much
water you will be introducing into the enclosure so they can provide
adequate drainage capabilities.  

Remember if you go below a certain size orifice (I think it's 3/8") you
will have to provide a strainer on the system.  

Don't forget to discuss system interlocks for belt movement interruption
with the conveyor vendor and owner.  

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Monday, February 02, 2009 6:49 PM
To: [email protected]
Subject: RE: Sprinkler protection below conveyors in pits

We have used nozzles that can be selected with various spray patterns in
this situation. Also something that we have recently discovered is that
if this is an FM insured property they normally do not require the
return belt to be covered even though NFPA is clear that it should be.
If not FM then we find a solution that most closely complies the
standard and listing and present that to the powers to be. It is not
always possible to comply 100%.

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ryan
Hinson
Sent: Monday, February 02, 2009 3:56 PM
To: [email protected]
Subject: Sprinkler protection below conveyors in pits

Where would I go to properly protect below conveyors in pits that there
is less then 4' of clear space below the return loop of the conveyor and
the conveyer belt is 60" wide with SSU's?  NFPA 13(2002) section 8.6.5
does not address this situation in my opinion.  What is the space depth
at which sprinklers are no longer able to develop the water pattern
necessary to be practicable?



Thank you,



Ryan L. Hinson, EIT, CET, Nicet III

FP Design Manager

Fire Construction Design Services, LLC #C124

A Division of Fire Construction Services, Inc.

6950-43rd Avenue SE

St. Cloud, MN 56304

Direct:  320-250-5404 

Fax: 320-358-3495

email:  <mailto:[email protected]>
[email protected]



CONFIDENTIALITY NOTICE: The information contained in this message,
including any files transmitted within, is confidential, may be legally
privileged, and is intended only for the use of the individual(s) named
above. The use of any confidential or personal information may be
restricted by state and federal privacy laws.  If this message was
received in error, please notify the sender and then delete this
message.



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)