He is requiring us to cover the area.

Thanks,
 
Chris Russell

t. 360.734.4940
f. 360.647.9540
securitysolutionsnw.com 
 

-----Original Message-----
From: Jay Jay Blocker [mailto:[email protected]] 
Sent: Thursday, February 05, 2009 9:48 AM
To: [email protected]
Subject: Re: IFC vs NFPA 13 issue

Is he stating that he is going to require you to protect this area or just
asking for clarification?
 
Jeremy S. Blocker
 
Let us not look back in anger, nor forward in fear, but around in
awareness. --James Thurber 




________________________________
From: Chris Russel <[email protected]>
To: [email protected]
Sent: Thursday, February 5, 2009 9:21:00 AM
Subject: IFC vs NFPA 13 issue

Hello,

I have a disagreement with the fire marshal and I would like another
opinion. I have a prefabed metal building framed with sheet metal studs in
all areas but the elevator shaft which is a 2 hour fire wall made of wood
and sheetrock. 



We omitted sprinklers in the area above the t-bar lid per NFPA 13/2002
8.14.1.2.1 because this area is of noncombustible construction and limited
combustible construction.



The fire marshal has stated that limited combustible construction is not
allowed per the IFC per the following code. 

IFC section 903.3.1..1 - NFPA 13 sprinkler systems.

Where the provisions of this code require that a building or portion of
thereof be equipped throughout with an automatic sprinkler system in a
accordance with section 903.3.1.1, sprinklers shall be installed throughout
in accordance with NFPA 13 except as provided in Section 903.3.1.1.1.

903.3.1.1.1 - Exempt locations

Automatic sprinklers shall not be required in the following rooms or areas
where such rooms or areas are protected with an approved automatic fire
detection system in accordance with section 907.2 that will respond to
visible or invisible particles of combustion. Sprinklers shall not be
omitted from any room merely because it is damp, of fire-resistance rated
construction or contains electrical equipment. #4 In rooms or areas that are
of noncombustible construction with wholly noncombustible contents.



It is my opinion that 903.3.1.1.1 addresses areas exempt from 903.3.1.1 i.e.
exceptions to the requirement of an NFPA 13 system. This does not mean that
areas exempt from coverage in NFPA 13 must conform to IFC 903.3.1..1.1. 



Thanks,



Chris Russell



t. 360.734.4940
f. 360.647.9540

securitysolutionsnw.com 


      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to