Another thought is VESDA and sprinkler and skip the clean agent. Thought being VESDA gives early warning and they can do the ATC thing and investigate the "smell" with some safety margin. They probably should have fire extinguishers to handle incipient fires alerted to them from the VESDA. And if the fire gets big enough to set of sprinklers the equipment is most likely shot anyway. This should manage the life safety of the ATC people and those in their care in the air.
Next step is adding the clean agent but this is only to really protect the equipment. I'm not seeing a big increase to life safety here. So someone needs to make a judgment on the cost of clean agent vs. the equipment. Another consideration is this JFK or Atlanta or some other busy place or St. Cloud regional that does a handful of IFR flights a day and only really need a tower when they are below VFR weather minimums. Having 100 planes scatter around JFK vs. 2 around St. Cloud is a big difference. Being a pilot myself when it's just 2 of us and faced with an unexpected tower closure I'm not very concerned for my safety in the plane even if in the clouds. Remember there is a plus side to fire in that it forces one to upgrade to the most modern equipment. If my house burns I can't get a CRT any more right, force me to finally break down and by a LCD or the like. Also forces me to retrofit the house with sprinklers but that's another issue in this hypothetical. Perhaps the air traffic authorities (or any other entity) are derelict in maintaining a safe environment because they don't have the money to upgrade but have the money to replace after a fire. Sort of combining two human conditions and a little morphing - time to do it over but not right in the first place and planned obsolesce. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Friday, February 13, 2009 5:14 PM To: [email protected] Subject: RE: you be the engineer here First and foremost, I am not an engineer, so I don't even begin to fall into your inquiry of being the engineer... That being said, I have only worked on one relatively small control tower. It was approximately 82' high and per the owner's request, the engineer of records signature, and the AHJ's blessing we only provide a fire pump and class III stand pipe. I believe that they were very concerned about their very expensive equipment and felt that the 1-1/2" hose would be enough if an emergency ever arose. Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of å... .... Sent: Friday, February 13, 2009 3:53 PM To: [email protected] Subject: you be the engineer here there is no right or wrong answers. i have seen several different offered up in different locations and different countries... which struck me as curious since this is such a serious and mission critical location. so it seemed this forum's collective imagination and experience with systems that work and do NOT work, might benefit those that fly. again, no right or wrong answers. just comparing alternatives. scot deal excelsior No virus found in this outgoing message. Checked by AVG - www.avg.com Version: 8.0.233 / Virus Database: 270.10.23/1951 - Release Date: 02/13/09 06:51:00 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)