I'm nowhere close to being a PE, but I can't help myself.  I'd kindly replay
"Gladly and ASAP, as soon as you approve the change order."

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Fletcher, Ron
> Sent: Wednesday, February 25, 2009 4:03 PM
> To: [email protected]
> Subject: PE Peer Review
> 
> I would like the take from the PE's on forum on how to deal with a plan
> review comment from an unnamed engineering firm (RJA).
> 
> "Due to the higher than normal potential for a fire in the occupant
> sleeping and common areas, the reduction in fire are (remote area) for
> quick response sprinkler in accordance with NFPA #13 Figure 11.2.3.2.3.1
> is not a good engineering practice. Please revise the hydraulic
> calculation to account for at least the minimum 1500 square foot design
> area as specified by NFPA #13."
> 
> The hazard is a dormitory at a minimum security prison.
> 
> Ron Fletcher
> Aero Automatic Sprinkler
> Phoenix, AZ