A common misconception, based on the requirements of IBC, Chapter 16. In fact, NFPA 13, 2007 requirements for seismic bracing are in accordance with ASCE 7 provisions and are compliant with the intent of Chapter 16. We fight this confusion and overlap on nearly every state-jurisdiction project we do these days. It is NOT the intent of the IBC to make special considerations for sprinkler systems, which is why the code specifically references NFPA 13 in Chapter 9.
IMHO. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Joe Powell Sent: Friday, March 13, 2009 10:09 AM To: [email protected] Subject: Siesmic - NFA 13 vs IBC A seismic vendor was in our office this week claiming that IBC 2006 no longer accepts NFPA 13 for seismic bracing of sprinkler piping. Sprinkler piping is subject to rules and exclusions of other piping systems. Anyone else heard of this? Joe C. Powell Pruett Ford & Associates, Inc. Consulting Engineers 1201 Broad Street, Suite 3A Augusta, GA 30901 Ph: 706-722-3959 Fax: 706-724-5127 Email: <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3935 (20090313) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 3935 (20090313) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)