George,

I have designed several pumps with flow meters and never put a check valve
on the discharge side of the meter.  Looking at NFPA 20 (2007) Fig.
A.5.19.1.2(b) does not indicate a check valve in the test loop.  So if this
is a requirement it is news to me.  The meters we use are a venture type, so
backflow shouldn't cause a problem as there isn't anything to damage.  Are
you using a turbine type meter?

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: George Medina Jr [mailto:[email protected]] 
Sent: Wednesday, March 18, 2009 2:04 PM
To: [email protected]
Subject: Check Valve On Discharge side of Flow Meter

NFPA No.:Z4Pump02 page 108 - States that a check valve is required on the
discharge side of flow meter. Our union field guys state they never put one
on?there. Is this correct?
I believe a flow meter would be damaged from positive city pressure back
flowing through the meter after shutting down the pump and before closing
the isolation valve. Somebody correct me for being wrong.


George Medina Jr.
Sr. Fire Sprinkler Designer
Dorvin D. Leis Inc.
Honolulu, HI 96819

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to