As a change of subject, kind of.
Why does NFPA 13 report no minimum air pressure when doing a cold weather 2 hour test. (16.2.1.3, 02 edt) NFPA 14 states 40 psi for cold weather test. (9-4.1, 00 edt.) NFPA 25 states 25 psi for test of existing dry standpipes. (6.3, 02 edt) 25 commentary discusses the potential high pressure from the air. The same reason that we do not air test plastic. I was just curious as these look like some more numbers snatched from air. <- Get It? R/ Matt Matthew J. Willis Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)