There is probably less detail because CPVC is usually field cut and 
steel is (can be) pre-fab. That being said, they should meet the 
requirements of chapter 14, whatever the material. Another issue is 
that CPVC systems tend to go into stick-built residential buildings. 
The framing of these is frequently not known until after they are 
constructed and changes need to be made to adapt. (I did a condo 
complex a few years back with 3 "typical" buildings. Each building 
was done by a different framing contractor and the style was 
different enough that the buildings were no longer typical)


At 11:02 AM 3/26/2009, you wrote:
>Along that same line:
>
>Why is the quality of "plastic" drawings always less than "steel" 
>drawings? I always fought with my bosses over this. NFPA Chapter 14 
>(2002, Edition) makes has no different requirement for the two.
>Should I disapprove plastic drawings (think - cocktail napkins) that 
>do not fulfill the requirements of Chapter 14?
>
>As for the as-built question: Don't send me any, I don't have the 
>room or the time to deal with them.
>"Don't want 'em, Don't need 'em, Got no use for 'em"
>
>David Autry
>Plans Examiner
>Nebraska State Fire Marshal's Office
>246 S. 14th Street
>Lincoln, NE 68508
>402-471-9659
>402-471-3118 fax
>www.sfm.ne.gov
>
>** Note new email address: [email protected]
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of 
>[email protected]
>Sent: Thursday, March 26, 2009 9:46 AM
>To: [email protected]
>Subject: RE: Does NFPA 13 require as-built drawings
>
>I'm not sure I understand.  What part of NFPA 13 says that you don't
>have to leave behind accurate system documentation?  Yes, it seems to me
>there are a few steps in this process, and sometimes it's inconvenient
>and time consuming to take all those steps, but, again, where does it
>say you leave behind something that doesn't match what you installed,
>including the AHJ approval?
>
>Maybe I'll turn this around and ask what items on the NFPA 13 working
>drawing / hydraulic calc lists have to be correct, and what items can be
>approximate and maybe corrected later on another set of documents called
>"as-builts", but only if you find a requirement to submit as-builts?
>
>Bill Brooks
>
>William N. Brooks, P.E.
>Brooks Fire Protection Engineering Inc.
>372 Wilett Drive
>Severna Park, MD 21146
>410-544-3620 Phone
>410-544-3032 FAX
>412-400-6528 Cell
>
>-------- Original Message --------
>Subject: RE: Does NFPA 13 require as-built drawings
>From: <[email protected]>
>Date: Thu, March 26, 2009 10:12 am
>To: <[email protected]>
>
>You got it bucko! Con sarnt contraktors always trying to cheat the
>system out of its due! It's downright Un-American to not follow the
>plan, people got ta eat ya know! ;)
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC 29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Fletcher,
>Ron
>Sent: Thursday, March 26, 2009 10:03 AM
>To: [email protected]
>Subject: RE: Does NFPA 13 require as-built drawings
>
>So we should submit preliminary plans and get them permitted (A.22.1),
>submit working plans and get them approved (22.1.1 & A.22.1), get the
>permission of the AHJ every time we deviate from the approved working
>plan (22.1.2) and after all our deviations are approved we should submit
>the "corrected working plans" (Bill Brooks) for approval?
>
>Ron Fletcher
>Aero Automatic Sprinkler
>21605 N. Central Ave
>Phoenix, AZ 85024
>P: 623.580.7836
>F: 623.434.3420
>C: 602.763.4160
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of George
>Church
>Sent: Thursday, March 26, 2009 12:49 AM
>To: [email protected]
>Subject: RE: Does NFPA 13 require as-built drawings
>
>Then there's the contractual thing, where they make minor changes like
>the ceiling guy turns the pattern 90* or shifts it, but they don't want
>to pay you to make the change. Why should we?
>
>Glc
>Under 2002 #13 still.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
>Williams
>Sent: Wednesday, March 25, 2009 8:01 PM
>To: [email protected]
>Subject: RE: Does NFPA 13 require as-built drawings
>
>Reality check. "As-builts" are a separate document. They are usually
>generated from the original design drawing and the fitter's field notes
>(if he kept them). As to an as-built being exact - good luck.
>Contractors may keep some notes on what they change, but they are hardly
>an EXACT duplicate of what is installed (and the assumption is that the
>designer has access to them). Consequently, as-built drawings at best
>give you an idea of major changes (main and sprinkler locations) but are
>far from perfect. There is not enough money or time in any design job
>for the designer to go out and map out every piece of pipe installed.
>"If pipe lengths and fittings have changed..."? Outside of number of
>heads, what else would change? So every job would have to be re-calced.
>Also, if we have to wait for AHJ approval before any changes are made
>(22.1.2), nothing will ever get finished. In a perfect world, you are
>right, but this ain't a perfect world.
>
>
>At 07:34 PM 3/25/2009, you wrote:
> >I think the "as-built" term is a commonly used misnomer, somehow
> >distinguishing the document used to install a system from some "extra"
> >document you leave behind for the owner to use later. The proper term
> >for "as-built" should be "corrected working plan" representing the
> >completion of something that's required from the beginning. I'm not
> >saying the as-built has to be cadded up like the original. NFPA 13 is
> >silent on this. However, the drawing left behind has to be EXACTLY
>what
> >is installed, and that redlined drawing has to have the AHJ approval in
> >some manner (22.1.2). If pipe lengths or fittings have changed, then
> >"corrected hydraulic calculations" are also required. Otherwise the
> >installer has been paid but hasn't completed the job.
> >
> >Perhaps our frequent AHJ contributors could weigh in on this one as
> >well.
> >
> >Bill Brooks
> >
> >William N. Brooks, P.E.
> >Brooks Fire Protection Engineering Inc.
> >372 Wilett Drive
> >Severna Park, MD 21146
> >410-544-3620 Phone
> >410-544-3032 FAX
> >412-400-6528 Cell
> >
> >-------- Original Message --------
> >Subject: RE: Does NFPA 13 require as-built drawings
> >From: "larryshulman" <[email protected]>
> >Date: Wed, March 25, 2009 6:11 pm
> >To: <[email protected]>
> >
> >Working plans are for the installation phase, while the "as-built" set
> >is intended for use following the installation. That's why NFPA 13 is
> >silent on the as-built requirement but it appears in NFPA 25.
> >
> >I agree this appears somewhat awkward, but I suppose there's logic in
> >there somewhere. When you find it, so advise:)
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of
> >[email protected]
> >Sent: Wednesday, March 25, 2009 2:45 PM
> >To: [email protected]
> >Subject: Re: Does NFPA 13 require as-built drawings
> >
> >Okay, but NFPA 25 pertains to maintenance of systems, not installation.
> >I understand NFPA is saying: IF there are as-builts, they will be
> >stored, etc.
> >
> >Forest Wilson
> >
> >Project Manager
> >Cherokee Fire Protection Co.
> >3195 Dayton Xenia Rd Ste 900
> >Dayton OH 45434
> >
> >ph: 937-376-2333
> >fx: 614-455-4324
> >cell: 937-307-5647
> >
> >Visit our blog: _www.cherokee-fire.blogspot.com_
> >(http://www.cherokee-fire.blogspot.com/)
> >
> >
> >FIRE SPRINKLERS SAVE LIVES!!
> >
> >
> >
> >NOTICE: The information contained in this email is intended to be
>solely
> >for
> >the use of the named individual or entity to which it is directed and
> >may contain information that is privileged or otherwise confidential.
> >It is not
> >
> >intended for transmission to, or receipt by, anyone other than the
>named
> >addressee (or a person authorized to deliver it to the named
>addressee).
> >It
> >should
> >not be copied or forwarded to any unauthorized persons. If you have
> >received this electronic mail transmission in error, please delete it
> >from your system without copying or forwarding it, and notify the
> >sender of the error by reply email or by calling Cherokee Fire
> >Protection Co. at 888-347-3079 toll free.
> >
> >
> >
> >In a message dated 3/25/2009 5:44:36 P.M. Eastern Daylight Time,
> >[email protected] writes:
> >
> >Actually you'll find it in NFPA 25 as follows:
> >
> >" 12.3.2 As-built system installation drawings, original acceptance
>test
> >records, and device manufacturer's maintenance bulletins shall be
> >retained to assist in the proper care of the system and its
> >components."
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
> >[email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >
> >**************Great Deals on Dell 15" Laptops - Starting at $479
> >(http://pr.atwola.com/promoclk/100126575x1220635228x1201407499/aol?redi
>r=ht
>t
> >p:%2F%2Fad.doub
> >leclick.net%2Fclk%3B213153654%3B34689672%3Bo)
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
> >[email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
> >[email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
>[email protected]
> >
> >To Unsubscribe, send an email
>to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to