I've reread (several times) the proposed change to 7.3.2(5) and I think I
now understand the intent.  But I'm still confused.  

The proposed change to A.7.3.2 (also part of 14-53 Log#CP3) adds a sentence
that reads "Only one standpipe is necessary to serve the roof, it is not the
intent to extend each standpipe to the roof level."  

OK, let's say we have 3 stairways and 3 standpipes.  Stairway 1 has roof
access, stairway 2 & 3 don't.  Per 7.3.2(5), we install a valve at the
highest landing in stairway 1.  Per 7.3.2(5), we install a valve above the
roof at stairways 2 and 3.  So I'm having a hard time understanding how
"Only one standpipe is necessary to serve the roof, it is not the intent to
extend each standpipe to the roof level" should be interpreted. I don't see
anything in 14-53 Log#CP3 that mentions testing.

Ed Kramer
Littleton, CO


 
> The intent of CP #3 is to clarify the intent that there only needs to be
> a single roof connection to facilitate testing.   The language remains
> regarding a connection at the highest landing of stairs serving roof
> access.  Many AHJ's will require manifolds at the top of all standpipes
> arbitrarily, as they perceive a potential value in suppression
> operations.
> 
> Steve
> 