I suspect the prior response was attempting to point out that the  
listing is for smooth construction (excluding the beamed listing) and  
a ceiling pocket kinda messes that up.  So to use residential  
sprinklers in such arrangements, it has to be allowed by 13 /13R.   A  
related example is the use of sidewall sprinklers beneath overhead  
doors.  Not listed for such uses but now allowed by 13.

Roland

On Apr 6, 2009, at 11:13 AM, Eric Tysinger wrote:

> The ceiling pocket rules in NFPA 13/13R/13D only tell you when you  
> need / don't need sprinklers. The ceiling pockets rules are not  
> considering the "pocket" areas as protected. Therefore the  
> residential sprinkler installed in the lower ceiling are per  
> manufacturers guidelines. When the ceiling pocket rules require the  
> pocket to be protected then the residential sprinkler must be  
> installed per manufactures spec.
>
> Let's look at NFPA 13, it allows for pockets up to a maximum of 36"  
> deep. What standard sprinkler is listed to 36" down.
>
> As long as the pocket meets the requirements of NFPA 13/13R/13D for  
> omitting the sprinkler protection then the depth is not a factor,  
> only floor coverage is required.