-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Tuesday, April 07, 2009 10:57 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

Where we are, the electrical inspector does not allow us to enter in and
back out of electrical rooms. We can pipe in with pipe for sprinklers
but we can not exit out. This includes bringing UG through the floor and
exiting through a wall or ceiling. It's kinda like the roach motel -
roaches check in but they don't check out!

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
[email protected]
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, April 07, 2009 9:46 AM
To: [email protected]
Subject: RE: Pipe passig thru Electrical Equipment Rooms

The pipe is allowed to pass through the electrical room.  However there
were restricted spaces within the rooms over or in front of certain
equipment where the pipes were not permitted to be run.

Is your electrical room sprinklered?

If it is not it must meet the criteria set forth in #13 and in the
Building code otherwise it is to be sprinklered:
a. 2 hour fire-rated enclosure including protection for penetrations.
b. Only dry type electrical equipment is used.  (you need to ask, don't
assume this one) c. The room is dedicated to electrical equipment only.
d. No combustible storage is permitted to be stored in the room.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eladio N.
Alvarado
Sent: Tuesday, April 07, 2009 8:42 AM
To: [email protected]
Subject: Pipe passig thru Electrical Equipment Rooms

Forum:
I think that this subject may have been previously discussed a long time
ago, but I can't remember the final judgment, thus, the question is, how
does one justify passing pipe thru electrical or similar type rooms when
its prohibited by the NEC code? This particular installation is to meet
# 13, Light Hazard, and the local authority has no problem with it, and
the rooms have Fire Sprinklers in them, which are mandated by the
locals. The objection comes from the EOR. Help would be greatly
appreciated.

Eladio Alvarado
AFSDI


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to