It is there but only under Group A plastics.  Easy argument to say  
it's reasonable to apply it to a lesser hazard.  You're still stuck by  
the 30 ft max storage height = 50 ft ceiling.

Roland

On Apr 10, 2009, at 10:21 AM, Daniel Merkle wrote:

> Roland,
> I see what you are talking about in 12.1.3.4.1(2007).
> What if you are still using 2002?
>
> Daniel L. Merkle, CET
>
>
>
>
>
>
> ________________________________
> From: Roland Huggins <rhugg...@firesprinkler.org>
> To: sprinklerforum@firesprinkler.org
> Sent: Friday, April 10, 2009 1:14:06 PM
> Subject: Re: Storage Sprinkler
>
> As the criteria says, you artificially assign a storage height so that
> you have a 20 ft clearance.  That is inherently limited, though, by
> solid pile having a maximum storage height so a 50 ft ceiling is about
> it.  Beyond that you are then back to the previously mentioned ceiling
> installation business.
>
> Roland
>
> On Apr 10, 2009, at 10:00 AM, Daniel Merkle wrote:
>
>> Ron,
>> You are correct. It is solid pile and what concerns me is I could
>> not find any limit on clearance from top of storage.
>>
>>
>>
>>
>>
>> ________________________________
>> From: "Fletcher, Ron" <rfletc...@aerofire.com>
>> To: sprinklerforum@firesprinkler.org
>> Sent: Friday, April 10, 2009 12:57:20 PM
>> Subject: RE: Storage Sprinkler
>>
>> He said it was solid pile. Is there a limit on clearance from top of
>> storage for area density in 07?
>>
>> Ron Fletcher
>> Aero Automatic Sprinkler
>> 21605 N. Central Ave
>> Phoenix, AZ 85024
>> P: 623.580.7836
>> F: 623.434.3420
>> C: 602.763.4160
>>
>> -----Original Message-----
>> From: sprinklerforum-boun...@firesprinkler.org
>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
>> Huggins
>> Sent: Friday, April 10, 2009 9:49 AM
>> To: sprinklerforum@firesprinkler.org
>> Subject: Re: Storage Sprinkler
>>
>> Listen to Steve but support it with the 2010 ROC.  We did a lot of
>> work to explicitly address excessive clearance for spray sprinklers  
>> in
>> storage under section 12.1.3.4 currently titled Ceiling Heights
>> (changed that too).  The current criteria won't fly because it is
>> limited to solid pile (as shown by the approach coming from the old
>> NFPA 231) and Class I-IV in racks less than 25 ft (though that became
>> clear only at the ROC).  Section 12.1 kills using it for all
>> storage.   The option to put a barrier over the rack with sprinkler
>> beneath them (tough option) was deleted.
>>
>> Roland
>>
>> On Apr 10, 2009, at 9:21 AM, Steve Leyton wrote:
>>
>>> In-racks baby!   Sell sprinkers!
>>>
>>> Steve Leyton
>>> Protection Design & Consulting
>>> San Diego, CA
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> techsupp...@firesprinkler.org
>>
>> To Unsubscribe, send an email
>> to:sprinklerforum-requ...@firesprinkler.org
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>
>> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
>> (Put the word unsubscribe in the subject field)
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>
>> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to