Relying solely on 13R may give you righteous reason for outrage at the
official, but you may want to look carefully at 6.1.4.4 protection of
risers, if it is risers he is asking you to protect. And also look at
6.2.7(17) submission requirements for "Protection of nonmetallic pipe".

An just as a final aside, IBC/IMC/IPC/IEC all require additional protection
of all system components when there is less than an 11/2" of wood from the
face of the stud to the hole, pipe, wire or service.