Randy, My take on this is yes, your deck/balcony is a similar small unheated area as described in the annex. So long as your deck/roof doesn't exceed 7'6" in depth this should apply. Another point that seems applicable is that a loading dock will often contain a greater degree and quantity of combustible product then the average balcony.
Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Randy Knutson Sent: Friday, April 24, 2009 2:16 PM To: [email protected] Subject: IFC Balcony protection in 13R occupancies Fellow Forum Members, Can a dry pendent sprinkler in the orientation as shown in 13:A.8.15.7 2007ed be used for a balcony protection as required in the IFC? Thanks in advance, Randy Knutson _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)