Randy,
My take on this is yes, your deck/balcony is a similar small unheated area
as described in the annex.  So long as your deck/roof doesn't exceed 7'6" in
depth this should apply.  Another point that seems applicable is that a
loading dock will often contain a greater degree and quantity of combustible
product then the average balcony. 

Bob Knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Friday, April 24, 2009 2:16 PM
To: [email protected]
Subject: IFC Balcony protection in 13R occupancies

Fellow Forum Members,

 

Can a dry pendent sprinkler in the orientation as shown in 13:A.8.15.7
2007ed be used for a balcony protection as required in the IFC?

 

Thanks in advance,

 

Randy Knutson