I think that the 15' rule would apply in this situation. See NFPA 13(07) 
12.3(1).

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ryan Hinson
Sent: Monday, April 27, 2009 4:29 PM
To: [email protected]
Subject: Noncombustible concealed space?

I have a noncombustible space above light hazard occupancy suspended ceiling 
tile with 4" clearance from the bottom of the tee channel to the bottom of the 
purlins.  The purlins are 10½" deep and spaced at 5' OC with the roof pitched 1 
in 12.  The wall edge at the high point parallel to the purlin goes to the 
deck.  The wall perpendicular to the purlins running down the slop only goes to 
the bottom of the purlin.  The other two walls are exterior walls.  Do I need 
heads above the ceiling tile protecting the noncombustible space above since 
the wall is not to the deck?  The space not above the suspended ceiling tile is 
OH II hazard.  Nothing is nor should be stored in this space.  Do I need to 
protect beyond the OH II and over the light hazard a certain distance?  I can't 
find if/where its addressed in NFPA 13(2002).  We're talking 5 openings  above 
the wall and into the annular space between purlins of 10½" x 5'-0" all on one 
wall to 5 partially separated voids of 168.6 cubic feet.  What say you?

Thank you,

Ryan L. Hinson, EIT, CET, Nicet III
FP Designer
Big Sky Fire Protection, Inc.
831 Cerise Road
Billings, MT 59101
Direct:  (406)294-9775 
Fax:  (406)256-5933
Cell:  (406)794-1552
email:  [email protected]
 
CONFIDENTIALITY NOTICE: The information contained in this message, including 
any files transmitted within, is confidential, may be legally privileged, and 
is intended only for the use of the individual(s) named above. The use of any 
confidential or personal information may be restricted by state and federal 
privacy laws.  If this message was received in error, please notify the sender 
and then delete this message.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to