CM? at the roof?

-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Steve
Leyton
Sent: Tuesday, June 16, 2009 9:35 AM
To: [email protected]
Subject: RE: Carpet Pad Storage


If I'm not mistaken, the carpet padding takes you out of ESFR right away
because of inherent obstruction within the array (no longitudinal flues
possible).    And portable racks are a challenge to in-racks, I suppose
...    We've done probably 4 or 5 warehouses that were either dedicated
to or had significant flooring inventories, including and especially
rolled carpets and pads and all have used CM at the roof with in-racks.
One of them actually started under an ESFR system that we deconstructed
and converted back to spray sprinklers, in order to get to the in-rack
arrangement.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Tuesday, June 16, 2009 9:29 AM
To: [email protected]
Subject: RE: Carpet Pad Storage

Who is the insurance company? They would probably 
have something to say about it. I'd start there.


At 11:54 AM 6/16/2009, you wrote:

>Question: How to most effectively protect the following -
>
>*       Carpet pads (Group A plastic, expanded)
>*       Rolled and wrapped in plastic (non-encapsulated)
>*       On portable racks that are 7-feet high and 6-feet x 6-feet
square
>*       Client desires to stack them 2-high (14-feet)
>
>Building  is approximately 40-feet high (tilt 
>panel warehouse)with k-14 ESFR's calculated for 75 PSI (12 heads).
>
>The tenant space is fairly small at 30,000 
>square feet and includes some 25-foot tall 
>double-row rolled carpet racks (with in rack sprinklers per FM
criteria).
>
>Also contains some standard pallet racks with Class IV commodity to
25-feet.
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[email protected]
>
>To Unsubscribe, send an email
to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4159 (20090616) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4159 (20090616) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to