Question is, why two different temp ratings in the same common space?

Also if this is a warehouse and it's non-conditioned, what is the max. indoor 
temperature this area could experience?  165's might be a bit low? 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, June 17, 2009 11:59 AM
To: [email protected]
Subject: Temperature Rating

'07 8.3.2 Rating and 8.3.3 Sensitivity

 

I can find no place where is says what if anything should be done with 
different ratings in the same room (10,000 sq. ft. ish room).  8.3.3 clearly 
says when QR all in compartment must be QR.  But in the temperature rating 
there is nothing like that.  A.8.3.2.7 is close but only suggesting the high 
temps in high hazard go 30' beyond.  So at 31' one could change back to 
ordinary temp.  

 

The situation is an existing space OH design (mini-storage) with 286 heads, in 
one bay (2 lines) heads are 165 heads.  All standard response.  There is a beam 
separating the two temperature different heads.  The beam is 22" down
from the clg.  but the top 4" is open for the joist bearing.   A competitor
noted this temperature issue on an inspection as a deficiency.  We were the 
last one in there doing work <6 months ago but not in this area.  Fire Marshal 
wrote orders to the owner to fix based on inspection report.  Owner is wanting 
us to fix it, presumable at our cost.  But I don't see where this is a 
deficiency in the first place.  We can have a discussion about whether it's a 
good idea or not but in the end the code seems to allow the mixing of heads 
temperatures.  Yes skipping of heads at the interface is a potential issue.  
How much is a guess, me brain doesn't do CFD modeling.

 

Yes it's easy to say just change out the heads and make them all high temp.
We may do it but I am trying to establish all on the same page that this is 
perfectly CODE compliant then negotiate a fix if wanted.  This is especially 
true when other sprinkler companies are involved and appear to be wrong.  

 

So anyone have a code reason this isn't allowed?  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [email protected]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to