News to me, laying one out for bid now where we are adding heads to maybe
avoid the pump and tank.  Existing building, top clg. probably 50' above
street, 5/8" meter, 3/4 ug.  Don't know static yet.  A few extra heads will
probably be cheaper than a pump.   

Recall the base spacing in the original development was 12'x12' so your room
as an example would have had 6 heads back in the day.  

The reduction in flow is a matter of density.  Over the sq.ft. you are
putting the same amount of water with the reduced spacing.  It's wet stuff
on the red stuff that puts a fire out.  The EC needs more total water
because more of it is going the wrong direction as compared to a regular
coverage. Might even theoretically need more density because of the slight
delay in fusing time of the head.   I'd take any day less water but closer
to the fire as better protection. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Thursday, June 18, 2009 2:51 PM
To: [email protected]
Subject: RE: 13D Question 1988 Edition

Again, going from memory as well.  Isn't / Wasn't there something saying
that you need to use the fewest number of sprinklers able to protect the
area.  So, if you have a 20'x30' room, you need to use 2 sprinklers at
20'x20' spacing, instead of using 4 at 16'x16'.  Using 2 sprinklers, you are
calculating flowing 40 gallons for the 2 sprinklers vs 26 gallons for 2
sprinklers  with 4 heads in the room, both scenarios protecting the same
space.  Is that possibly what he is referring to?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Thursday, June 18, 2009 12:36 PM
To: [email protected]
Subject: RE: 13D Question 1988 Edition

Mike,
Going from memory, I don't have any standards with me, there is a
requirement for QR sprinklers not exceeding 4.  I believe that this is
actually a 13R requirement though.  Maybe this is the confussion.

Bob Knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike Cabral
Sent: Thursday, June 18, 2009 12:06 PM
To: [email protected]
Subject: 13D Question 1988 Edition

I have an AHJ that is telling a designer that there can not be 4 sprinklers
in a single compartment. I was told that he is working off an old standard
from 1988 or so. Anyone have recollection of this. 

Mike Cabral
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)




__________ NOD32 4168 (20090618) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to