You are allowed to move up to 1-ft. to avoid obstructions to discharge,
either along branch lines, or between lines, but not both at the same time.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken Holsopple
(forum)
Sent: Thursday, June 25, 2009 12:49 PM
To: [email protected]
Subject: ESFR Spacing NFPA 13 2002 vs. 2007

Dear forumites,

I have a situation on a building where have have been contracted to do the
addition. The building is 40'+ at the peak. The existing and new building
are all protected (to be protected) with ESFR. The problem is that the
existing layout consists of several places where the branchlines (running
perp. to the bar joists) are spaced greater than 10'-0". The increased
spacing runs anywhere from 10'-1" to 10'-9". Each of the existing sprinklers
does not exceed the 100 sq. ft. In reading NFPA 13 ('02) Section 8.12.2.2.3
I see that an additional 1'-0" is allowed along the branchline when trying
to miss obstructions created by trusses/barjoists as long as the listed
criteria is met. Note that this only allows moving ESFR ALONG the line. No
mention of increased spacing between lines till you get to Section
8.12.2.2.4. But this section only applies to running parallel with the
steel. I will also note that the equivalent in the 2007 edition expands
8.12.2.2.3 to include wind bracing (what I would call x-bridging and/or
Horizontal Bridging). But it still states that sprinklers can only be moved
along the line. The GC would like us to continue with the spacing of the
original layout. I am resisting. My contention is that no matter what, the
distance between the branchlines should not exceed 10'-0". Am I right in
questioning the additional spacing between the lines or am I being to
literal in my interpretation? 

Best Regards,
Ken Holsopple
Designer 
Rowe Sprinkler Systems, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to