Excess Pressure Pump, I have seen these in the St. Louis, Missouri area, at a 
warehouse that had about 130 psi static pressure. The reason for their use was 
to help prevent false alarms due to pressure surges in the system, which would 
simulate a water flow.



Here is a link that better describes the device: 
http://books.google.com/books?id=kZEz-ogMXGwC&pg=PA47&lpg=PA47&dq=excess+pressure+pump&source=bl&ots=LbbYgLvWsg&sig=rnvTM4SWhrc1SsMZYMBY3mVp4-Y&hl=en&ei=dcFISuLqC4imNtjGpaMB&sa=X&oi=book_result&ct=result&resnum=6





Yours truly,


FRANK J. HERRICK
CITY OF LEAWOOD FIRE DEPARTMENT
OFFICE OF THE FIRE MARSHAL
14801 MISSION ROAD
LEAWOOD, KS. 66224-9560





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Sunday, June 28, 2009 12:00 PM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 44, Issue 27



Send Sprinklerforum mailing list submissions to

          [email protected]



To subscribe or unsubscribe via the World Wide Web, visit

          http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

or, via email, send a message with subject or body 'help' to

          [email protected]



You can reach the person managing the list at

          [email protected]



When replying, please edit your Subject line so it is more specific

than "Re: Contents of Sprinklerforum digest..."





Today's Topics:



   1. Re: mercoid switch on wet riser  ([email protected])

   2. DoD UFC - 13R System Design (Update) ([email protected])

   3. RE: mercoid switch on wet riser  (Tom Duross)





----------------------------------------------------------------------



Message: 1

Date: Sat, 27 Jun 2009 14:11:24 -0400

From: [email protected]

Subject: Re: mercoid switch on wet riser

To: [email protected]

Message-ID: <[email protected]>

Content-Type: text/plain; charset="us-ascii"



The old Gamewell excess pressure pumps had a very homemade look about them. And 
that sounds like what is being described. Used to be required in Canada and 
parts of Europe don't know if they still are..



Richard





-----Original Message-----

From: Todd Williams <[email protected]>

To: [email protected]

Sent: Sat, Jun 27, 2009 12:37 pm

Subject: Re: mercoid switch on wet riser







Sounds like an excess pressure pump. These were used in areas with a

lot of pressure fluctuations to prevent false alarms. This was before

flow switches with delays. Gamewell was famous for these but

Firematic made a fairly simple version of the same thing. Some towns

(at least in this part of the world) required them







At 11:38 AM 6/27/2009, you wrote:

>I saw something which I do not understand and hope someone can explain

>this to me.

>A 35 year old wet system, manifold with 2 alarm valves. There is a

>electric flow switch on each riser, I think added recently.

>The valves were trimmed with the normal motor gongs, etc.

>The system side gauges are piped together between the two risers, with

>check valves, a mercoid switch labeled pump switch, and another mecoid

>switch labeled alarm switch.  On this piping there are 3 check valves

>and a small test cock, presumably for testing.

>There is a small pump with 1/2 in inlet from supply side of valve 2,

>which discharges into the pressure gauge piping described above.

>

>What is the purpose of this? Was it standard at one time?

>

>_______________________________________________

>Sprinklerforum mailing list

>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>For Technical Assistance, send an email to: [email protected]

>

>To Unsubscribe, send an email to:[email protected]

>(Put the word unsubscribe in the subject field)



Todd G. Williams, PE

Fire Protection Design/Consulting

Stonington, Connecticut

www.fpdc.com

860.535.2080

_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]



To Unsubscribe, send an email to:[email protected]

(Put the word unsubscribe in the subject field)







------------------------------



Message: 2

Date: Sat, 27 Jun 2009 13:20:31 -0700

From: [email protected]

Subject: DoD UFC - 13R System Design (Update)

To: [email protected]

Message-ID:

          
<20090627132031.549a35b4b357aaf0be1435c7563e30f7.08742f8e71....@email.secureserver.net>



Content-Type: text/plain; charset="utf-8"



For those interested in the UFC 3-600-01 design approaches, I received

an informal opinion on the appropriate method to apply NFPA 13R

calculation methods.  Of course this is based on using NFPA 13R for the

correct buildings in the first place.



1.  Inside the dwelling unit use NFPA 13R.

2.  Outside the dwelling unit use NFPA 13R and any references to NFPA

13.

3.  A four head corridor calculation in the dwelling unit is acceptable

(see NFPA 13, Figure A.11.3.1.2).

4.  No hose stream is necessary.



Last, no fire department connection is required.



The project RFP or project plans and specs could overrule any or all of

the above and local installation guidelines might also differ.



Bill Brooks



William N. Brooks, P.E.

Brooks Fire Protection Engineering Inc.

372 Wilett Drive

Severna Park, MD 21146

410-544-3620 Phone

410-544-3032 FAX

412-400-6528 Cell











------------------------------



Message: 3

Date: Sun, 28 Jun 2009 10:51:04 -0400

From: "Tom Duross" <[email protected]>

Subject: RE: mercoid switch on wet riser

To: <[email protected]>

Message-ID: <[email protected]>

Content-Type: text/plain;   charset="us-ascii"



What Todd said.  They probably replaced the original compound type with a

mercury one.

>From what I know, Gamewell isn't making them anymore.  I think they ceased

last summer, I drove out to get a diff. switch and they told me.

Just as an aside, my grandfather is on the patent for this and a few other

things Gamewell made before and after the depression when they were in

Newton, MA.  I have a beautiful one I "kept" in my basement along with a

couple of those McCullough type switches I posted about last summer too in

really nice shape.

Of course, nothing official but my Dad has a picture of him and the crew

taken in the shop after another patent was awarded.  Funny coincidence.  :)



TD

Go Red Sox!



The old Gamewell excess pressure pumps had a very homemade look about them.

And that sounds like what is being described. Used to be required in Canada

and parts of Europe don't know if they still are..



Richard





Sounds like an excess pressure pump. These were used in areas with a

lot of pressure fluctuations to prevent false alarms. This was before

flow switches with delays. Gamewell was famous for these but

Firematic made a fairly simple version of the same thing. Some towns

(at least in this part of the world) required them







At 11:38 AM 6/27/2009, you wrote:

>I saw something which I do not understand and hope someone can explain

>this to me.

>A 35 year old wet system, manifold with 2 alarm valves. There is a

>electric flow switch on each riser, I think added recently.

>The valves were trimmed with the normal motor gongs, etc.

>The system side gauges are piped together between the two risers, with

>check valves, a mercoid switch labeled pump switch, and another mecoid

>switch labeled alarm switch.  On this piping there are 3 check valves

>and a small test cock, presumably for testing.

>There is a small pump with 1/2 in inlet from supply side of valve 2,

>which discharges into the pressure gauge piping described above.

>

>What is the purpose of this? Was it standard at one time?

>







------------------------------



_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]



To Unsubscribe, send an email to:[email protected]

(Put the word unsubscribe in the subject field)





End of Sprinklerforum Digest, Vol 44, Issue 27

**********************************************


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to