Steve, 

How many truck loading berths in the loading rack? 

If using oscillating monitors you have to be very careful of trucks and 
structure shielding the application of AFFF onto the fire. We use deluge 
systems tripped with linear type heat detector(Protectowire), to provide 
reliability we have crossed zoned two linear heat detection circuits. Each 
circuit is spaced 1/2 the UL listing spacing.

The overhead deluge provides quick and complete coverage for the application of 
AFFF to the grade level fire including areas under the rack platforms and 
trucks and trailers. The last loading rack was for eight truck/trailer tankers 
at a time, with a product throughput of 16k barrels per month.  

Have a fire safe day.

Regards

Jim
   

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Kowkabany
Sent: Thursday, July 09, 2009 12:31 PM
To: [email protected]
Subject: Loading Rack Protection

Would anyone care to share what type of foam water suppression systems they
have had success with in fuel loading rack applications with or without
canopies?

 

I have designed deluge sprinkler foam water systems activated by cross-zoned
flame detectors in the past for racks with canopies, but I have a client who
wants to look at oscillating ground sweep monitors to protect the area under
the canopy.  I kind of like that idea, because it gives first responders
some ability to unlock the monitor and spray other adjacent areas.  I'm
leaning towards the monitors also now that I am comparing all facets of each
system.

 

Has anyone had any experience with other arrangements they prefer?

 

Thanks very much,

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

616 Davis Street

Neptune Beach, FL 32266

904-652-4200 Phone

904-212-0868 Fax 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to