I sprayed the trim while we were up at 200 last summer, clapper up w/2x4,
ball drip removed.  No bubbles.  We did change the end of line last summer
because the old one was hissing from the packing.  It's a TestNDrain, not
that we needed all that but it's accessible in the attic and connects to
about 40' of galvy that runs down the outside of the building to a 45
plugged.  I sprayed the air line and fittings too and found nada BUT there
seems to be a slight leak into the intermediate chamber because both times
we got there, the drip cup was wet so maybe it's leaking back against the
water (wata)?  That could make sense.  Problem is it's 4" threaded out of
the room, above ceilings and inside walls until we see it in the attic.
Another problem is the old guy who was in charge retired and passed away a
couple of years before we got there and the new woman just isn't all that
knowledgeable.  My thinking was (and not my proudest moment), if I decrease
the air pressure the leak will slow down.  You'd think (at least I do) that
40 years of 3 year trips, accidental trips, and all that that the water
would rust up these old fittings.  They have records back 20 years anyway.
Maybe I'll offer to go and flood it and spray the heads?  We only walked
(well, crawled) the system when it was under 200, maybe I out to bring the
gas piping leak spray up to the attic.  Maybe it is a whole lotta small
ones?

Thanks,
Tom