Chris, you would be butting heads with every AHJ in the Central Florida 
area. I have never gotten a CO without sounding alarms within 60-90 secs.

Thomas Watt




----- Original Message ----- 
From: "Chris Cahill" <[email protected]>
To: <[email protected]>
Sent: Wednesday, July 15, 2009 11:53 AM
Subject: RE: water flow timing


> Right or wrong I always reconciled 13 vs. 72 like this.  The flow switch
> must activate within the parameters of 13.  5 minutes.  Once the paddle
> moves and the electrical connection is made 72 takes over and the FA must
> respond within the parameters of 72.  90 seconds.  So in theory 6.5 
> minutes
> could pass between opening the inspectors test valve and the alarm signal
> engaging in the FAP.
>